BR1500GI - High-pitched tone

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1500GI - High-pitched tone
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
7
2999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

BR1500GI - High-pitched tone

Having just recently purchased and set up a Back-UPS PRO - BR1500GI - Uninterruptible Power Supply 1500VA, I noticed that there is a faint, but noticeable and distracting high-pitched cyclical sound that lasts about 5 seconds, and then repeats. It sounds like this may be associated with continual charging of the battery, although the battery is fully charged. The serial number begins with '4A' if that is relevant. It is noticeable when there are no background noises and the room is otherwise silent.

Is a sound like this normal? 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

I think it's normal for them to make an audible noise when on battery, mine gives a thump and a low electrical hum.  As for the other noises, sounds to me like it's just an unfortunate characteristic of the components in your device.  I don't have one exactly like that so can't compare, but I'd say again if it disturbs you then see if you can do a warranty swap or something.  You'd probably have to discuss it with APC after sales support or whatever, I don't know if they actively monitor these forums.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

Sounds like a less than optimal capacitor to me, could be an early indicator of a future failure or just an unlucky noisy batch of components.  If it bothers you (I'm sure it would bother me) then consider asking APC for a replacement.  I have a Back-UPS ES 700 and it doesn't make any noise at all, except when it does a self-test when it goes a bit crazy with a loud whiney noise which reduces in frequency to clicks before becoming silent again, this could just be due to it's age as it's quite old now.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

Thank you for your suggestion.

So I engaged the APC tech support on chat today, and they asked me to take the AC + battery out, and power the UPS on for 5 seconds whilst completely unpowered to perform a reset. They apparently call this a Brain Dead procedure(!).

Interestingly, after that, whilst the UPS made the same noise as soon as it was plugged back in to AC, but switched off (presumably it still charges the battery in this state?), when I switched the UPS on again using the power button, the cyclic 5s pulsed noise went away.

Whereas before, the noise was on whilst the UPS was in the switched on state with a load.

Any idea what this change in behaviour means, if anything? Could it be associated with the device + battery being brand new and needing to settle down? I wonder why the reset procedure changed the sounds?

Now upon load I hear a sort of high-frequency hissing/static noise. I was able to make a recording of this (whereas the earlier noise did not seem to get picked up by my phone). 

https://photos.app.goo.gl/xShtFT2r9EN1hbrM9

Can you hear that with volume turned up? Is this normal? I have a feeling it might be.

Certainly this is far less distracting to me than the cyclic 5s pulsed tone I was hearing.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

My other (newer) UPS made that kind of hissing noise when switched on from being completely off and disconnected, it stopped after a while.  Possibly it could be the same components that were making the previous noise, only this time they caught a different amplitude / frequency or whatever.  Some transformers tend to hum, just like some monitors have a dead pixel or two, while still being within manufacturing tolerances.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

Good to know, thanks. When you say after having been switched on for a while, how long do you mean? Hours or days?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

Probably about 30 minutes, battery was at 74% so it must have been charging (now reads 100% and there is no noise).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

Cyclical tones are back. In general the unit just seems rather noisy.

I managed to create two videos that captures the 5s cyclic pulsed tone (but you may need to turn up volume to full).

Here is what it sounded like this morning:

https://photos.app.goo.gl/aY5JkL8CirxmzV7u5

Here is how it sounded when I switched it off and then back on. Notice how the cylical tone starts but then dies down, then it is just a sort of high frequency hissing.

https://photos.app.goo.gl/6AeShPXMr8eXT65B6

Here is the sound it makes when AC is switched off and it goes on to battery:

https://photos.app.goo.gl/NTyFhfcLjqffDVdx9

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

0 Likes
0
2999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:41 PM . Last Modified: ‎2024-03-26 03:00 AM

I think it's normal for them to make an audible noise when on battery, mine gives a thump and a low electrical hum.  As for the other noises, sounds to me like it's just an unfortunate characteristic of the components in your device.  I don't have one exactly like that so can't compare, but I'd say again if it disturbs you then see if you can do a warranty swap or something.  You'd probably have to discuss it with APC after sales support or whatever, I don't know if they actively monitor these forums.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore