Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BR1500G with new battery reporting low time

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1500G with new battery reporting low time
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:59 AM

0 Likes
3
3264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:59 AM

BR1500G with new battery reporting low time

I have a BR1500G and just replaced the battery with a new APC 124 battery pack.  I installed the battery and left it plugged in for 24 hours with no load.  But it reports much lower times than what it should.  With a 100W load it should last around 73 minutes.  But it reports about 53 minutes.  With a 700W load it should be 6 minutes but it reported 3 minutes.  

I read about a calibration routing but it was for SMART-UPS devices. It involved plugging in a 30% load or greater and make sure it never varies over 5% while you unplug the UPS and completely drain the battery.  I tried this with a 75% load but it was varying more than 5%. But it didn't seem to make any difference.  Any ideas?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
3264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

I tired that as well and it did seem to help.  The calibration was done with 31% range and it was a combination of fans and the few incandescent lights I still have.  I really don't anything else to plug in that would provide a consistent load.  

After all of this I got a load that was exactly 100 watts.  The battery time estimate on the front panel was 61 minutes.  I unplugged the UPS from the wall and it lasted 61 minutes.  The documentation from APC says it should last 73 minutes for a 100 watt load.  So that isn't too far off.   However when the unit is unplugged from the wall the output AC voltage drops from 121 to 113VAC and therefore the output wattage drops to watts.  You can see the lights dim and the fans slow a bit.  From the APC graph it should power a 90W load for over 80 minutes.  So I am only getting about 75% of the "advertised" time.   Is this just overly optimistic performance data from APC or is something wrong with my batter/unit?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
1
3264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

Hi Steven,

You may also wish to try changing the battery replacement date in the PCPE software and attempting the runtime calibration again with a load closer to the 30-40% range.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

0 Likes
0
3265
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:48 AM . Last Modified: ‎2024-03-26 03:58 AM

I tired that as well and it did seem to help.  The calibration was done with 31% range and it was a combination of fans and the few incandescent lights I still have.  I really don't anything else to plug in that would provide a consistent load.  

After all of this I got a load that was exactly 100 watts.  The battery time estimate on the front panel was 61 minutes.  I unplugged the UPS from the wall and it lasted 61 minutes.  The documentation from APC says it should last 73 minutes for a 100 watt load.  So that isn't too far off.   However when the unit is unplugged from the wall the output AC voltage drops from 121 to 113VAC and therefore the output wattage drops to watts.  You can see the lights dim and the fans slow a bit.  From the APC graph it should power a 90W load for over 80 minutes.  So I am only getting about 75% of the "advertised" time.   Is this just overly optimistic performance data from APC or is something wrong with my batter/unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

nyaAPCupss
nyaAPCupss
Explorer

Posted: ‎2025-04-21 08:09 AM

In response to BillP
0 Likes
0
1493
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-21 08:09 AM

Hello BillP,

I have the same problem. The software is no longer available on your website. There's PCSS software that replaced it, but it's only available for Windows. I don't have any Windows computers anywhere around me. What should I do next?

Thanks

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore