Hello,
Currently I have roughly 1.5-2 volts running through the ground/neutral coming out of a typical wall outlet. I need to get rid of this as it taking out some sensitive control boards I have. Currently I have the Back-Ups XS 1500. I was considering going up to the BR1500G but wanted to know if that model will eliminate the volts I currently have running through the ground/neutral? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:29 AM . Last Modified: 2024-03-22 12:40 AM
BR are cheap stand-by UPS, they have no effect over ground and neutral cabling besides filtering.
You should use an isolation transformer in order to regenerate neutral there are a couple models i think that come with smart RT UPS Models.
Normally a use a small dedicated isolation transformer.
I also recommend you check harmonic distortion levels.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:29 AM . Last Modified: 2024-03-22 12:40 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:29 AM . Last Modified: 2024-03-22 12:40 AM
Is there any unit that APC sells that will take care of the voltage I currently have going through the ground/neutral wire?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:29 AM . Last Modified: 2024-03-22 12:40 AM
BR are cheap stand-by UPS, they have no effect over ground and neutral cabling besides filtering.
You should use an isolation transformer in order to regenerate neutral there are a couple models i think that come with smart RT UPS Models.
Normally a use a small dedicated isolation transformer.
I also recommend you check harmonic distortion levels.