Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84245members
353345posts

BR1500G - Voltage Through Neutral/Ground

APC UPS for Home and Office Forum

Schneider Electric support forum for our APC offers including Home Office UPS, Surge Protectors, UTS, software and services and associated products designed to share knowledge, installation, and configuration.

Solved
Blind829_apc
Cadet
0 Likes
2
137

BR1500G - Voltage Through Neutral/Ground

This was originally posted on APC forums on 10/15/2010


Hello,

Currently I have roughly 1.5-2 volts running through the ground/neutral coming out of a typical wall outlet. I need to get rid of this as it taking out some sensitive control boards I have. Currently I have the Back-Ups XS 1500. I was considering going up to the BR1500G but wanted to know if that model will eliminate the volts I currently have running through the ground/neutral? Thanks.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
137

Re: BR1500G - Voltage Through Neutral/Ground

This reply was originally posted by Federico on APC forums on 10/18/2010


BR are cheap stand-by UPS, they have no effect over ground and neutral cabling besides filtering.

You should use an isolation transformer in order to regenerate neutral there are a couple models i think that come with smart RT UPS Models.

Normally a use a small dedicated isolation transformer.

I also recommend you check harmonic distortion levels.

See Answer In Context

2 Replies 2
Blind829_apc
Cadet
0 Likes
0
137

Re: BR1500G - Voltage Through Neutral/Ground

This was originally posted on APC forums on 10/18/2010


Is there any unit that APC sells that will take care of the voltage I currently have going through the ground/neutral wire?

BillP
Administrator Administrator
Administrator
0 Likes
0
138

Re: BR1500G - Voltage Through Neutral/Ground

This reply was originally posted by Federico on APC forums on 10/18/2010


BR are cheap stand-by UPS, they have no effect over ground and neutral cabling besides filtering.

You should use an isolation transformer in order to regenerate neutral there are a couple models i think that come with smart RT UPS Models.

Normally a use a small dedicated isolation transformer.

I also recommend you check harmonic distortion levels.