BR1300LCD - Continuous Beeping, Will it charge battery?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BR1300LCD - Continuous Beeping, Will it charge battery?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
123
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

0 Likes
3
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

BR1300LCD - Continuous Beeping, Will it charge battery?

Hi,

I just purchased two APC  UPS used, the BX1500LCD (says RS 1500 on front) and the BR1300LCD (XS 1300LCD markings).  I hope I have these model numbers correct.

Anyway, I am new to UPS.  I purchased these because I have a server and a home PC where I do my work, and I'm concerned about being able to save changes in the event of a power out.  We had a scare here over the winter where a lot of people lost their power.  We luckily didn't fall into that category, but it was nerve-wracking nonetheless.

The two UPS appear to power on correctly.  However, the BR1300 had a battery that reads 3.1v and 4.1v from its battery terminals.  Plugging this battery into the BX1500 makes the unit unable to function - it's LCD flickers and makes a ticking sound, and none of the buttons appear to be operable.


Plugging the low-v battery into the BR1300 (from whence it came) makes the unit produce a short beeping sound which seems to continue until the mute button is pressed.  

My primary question is --   Would this low voltage reading be something that could be produced just by the unit not being plugged in for a period of time?  Is this battery toast, or can I leave it in the unit and hope that it charges back up?

Other issues:  The battery which came from the BX1500 shows a full battery meter on the LCD.  Its terminals read 12v and 13v.  Is this the amount to be expected from these batteries? (they are 12v, right?)  

However, if I plug the (supposedly) good battery into the BR1300, it shows one "space" of the battery LED being charged (e.g. 20% charge).  Why would there be this discrepancy between the two units?

The batteries ARE the same for both units, right?  (They certainly look that way!)

Thanks for helping out a new fellow, as I'm a little befuddled about the entire situation - and having used devices definitely adds to the mire.

Sincerely,

Avery Freeman

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • br1300lcd
  • bx1500lcd
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

Avery,

That beep pattern and the flashing empty battery bar graph are both indicators of a "battery disconnect" meaning the unit is not recognizing the battery because it is too low voltage.  Most likely, this battery is too low voltage to fully charge, but you may attempt to let it charge for 24 hours and then run a self test to verify (again, I am not optimistic given the voltage you states as well as the battery disconnect beeping).

The serial number also notes this unit is from 2007 - batteries generally have a lifespan of 3 years depending on various use/storage factors, and the unit as a whole is on the older side as well.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

Hello Avery,

Yes both the units you have mentioned use the same battery (APCRBC109).  Do you happen to have the serial numbers of the units and do you know if the batteries were ever replaced?  Given that these units are discontinued, if the batteries were never replaced, they may require new batteries (especially since one is reading around 4vdc). Do you recall the beep pattern of the unit and any visual signals the unit gives (again most likely low battery)?

This manual may also help:  http://www.apcmedia.com/salestools/ASTE-6Z7VAU/ASTE-6Z7VAU_R0_EN.pdf?sdirect=true

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

Hi Jordan,

Thanks for the quick reply!  I did read the manual for both units, but I'm still not sure why they would act differently with the same battery in them -- why the BR1300 would give a beeping pattern, and why the BX1500 would just flicker and be unresponsive.

I definitely understand if I have to replace the battery, but again -- do you think it has a chance of charging up?  

I am leaving it plugged in now to see if it changes over time.  I thought I read lower voltage readings on the battery earlier today - around ~2v for each set of terminals - so I am thinking maybe it's charging up a little bit(?).

The beeping pattern produced by the BR1300 is a very short sequence of 2 quick beeps, which repeats in perpetuity after about a 2-3 second pause.  

The LCD battery meter outline flashes, and the meter has no "bars".  However, there is no "LOW" message which I thought the manual said would appear if it were a low battery.

Now that I'm looking at the serial number I realize I got the model number wrong.  It's a BX1300LCD.  My mistake!

The serial number is JB0703008288

Thanks again for your help!

Avery

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-27 02:28 AM

Avery,

That beep pattern and the flashing empty battery bar graph are both indicators of a "battery disconnect" meaning the unit is not recognizing the battery because it is too low voltage.  Most likely, this battery is too low voltage to fully charge, but you may attempt to let it charge for 24 hours and then run a self test to verify (again, I am not optimistic given the voltage you states as well as the battery disconnect beeping).

The serial number also notes this unit is from 2007 - batteries generally have a lifespan of 3 years depending on various use/storage factors, and the unit as a whole is on the older side as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore