I have a BN600 UPS that I am having some issues with. It had been a couple of years since I put a battery in it, and the power light was flashing, so I decided to replace the battery. I got a genuine APC battery, RBC17. After installing it I allowed it to sit with nothing plugged in for 24 hours to let it charge fully.
My issue is when I plug my Samsung laserjet into one of the battery back up outlets and I power up the printer the unit turns off (at least the green light goes out) and a solid alarm tone is sounded, and goes off until I hit the power button. It does not do this when I use on of the surge only outlets. only the battery back up ones. Does it sound like I got a bad battery, or does it sound like my unit has gone bad?
Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
Hi,
On 9/16/2017 6:26 PM, John said:OK. Does the constant tone mean that it is overloaded?
Yes. A constant tone will indicate an overload state.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
John,
Laser jets usually draw too much power for a battery backup unless it is a commercial / industrial unit
Your battery backup can only supply approximately 600 watts
A Laser printer can draw 1000 or more watts on startup
Your battery backup battery is ok if it can run a 100watt lamp for about about 6 minutes or more
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
OK. Does the constant tone mean that it is overloaded?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
You'd have to download the user guide for specifics on that particular unit.
It certainly could however
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:23 AM . Last Modified: 2024-03-27 12:09 AM
Hi,
On 9/16/2017 6:26 PM, John said:OK. Does the constant tone mean that it is overloaded?
Yes. A constant tone will indicate an overload state.
Link copied. Please paste this link to share this article on your social media post.