my old BK500MI (serial NB9828051536) always worked fine...but yesterday i came back home and it is beeping without any blackout occurring.
the power plug is in , the power socket is ok, the overload protector isn't popped , powering it off and then on: it restarts its beep-beep.
Battery measured about 12.2volts on a DVM then I replaced with a newer one from a CS350 (same capacity 7.2 Ah)
The beep-beep doesn't stop. It seems the ups can't go online but works ok on-battery and in the "surge protection only" outlet I measure 220VAC (right value for italy)
maybe some inside AC fuse blown?
Message was edited by: ziomarco
Message was edited by: ziomarco
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 AM . Last Modified: 2024-03-21 04:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 AM . Last Modified: 2024-03-21 04:35 AM
Hello to all the folks in the forum.
I think mr. largebattery is a spammer...let's go talking about my ups.
Today I opened the case and found the sitation shown in the attach file.
The varistor is clearly burned out.
Have I some hope of repair my ups by replacement of the varistor?
Thanks in advance for help.
ziomarco
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 AM . Last Modified: 2024-03-21 04:35 AM
As a senior battery application provider in mainland China, Dongguan Large Electronic Co., Ltd is always committed to serving industrial users, offering the most optimal battery solutions and supplying battery products with superior quality and competitive prices.Welcome to visit:http://www.large-battery.com to buy the quality lithium battery.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 AM . Last Modified: 2024-03-21 04:35 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:54 AM . Last Modified: 2024-03-21 04:35 AM
Hello to all the folks in the forum.
I think mr. largebattery is a spammer...let's go talking about my ups.
Today I opened the case and found the sitation shown in the attach file.
The varistor is clearly burned out.
Have I some hope of repair my ups by replacement of the varistor?
Thanks in advance for help.
ziomarco