Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BE650R-CN - can this run a self test?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE650R-CN - can this run a self test?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
144
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
jeffwiggins_apc
jeffwiggins_apc
Explorer

Posted: ‎2021-06-29 01:38 AM . Last Modified: ‎2024-03-22 03:13 AM

0 Likes
1
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:38 AM . Last Modified: ‎2024-03-22 03:13 AM

BE650R-CN - can this run a self test?

Hi,

I have a BE650R-CN model APC ups attached to my systems. I came home the other night and everything was turned off that was connected.. ie pc and router. when I tried to reconnect with the wall outlet. (trying to reboot it as it were). The ups emitting a long constant ringing. Not a beeping with intervals. I tested the ups by just plugging into a different wall outlet and a laptop running with the power connected. After being out for a couple of hours I came home and the laptop had powered down and the green light on the UPS was out. Power had drained from the laptop battery. It seems strange that it would drain even if the battery in the ups was bad.

Here is the current status output with nothing plugged into the ups.

DATE : Sat Aug 08 19:35:43 EDT 2009
HOSTNAME : m061839
RELEASE : 3.14.4
VERSION : 3.14.4 (18 May 2008) debian
UPSNAME : m061839
CABLE : USB Cable
MODEL : Back-UPS ES 650
UPSMODE : Stand Alone
STARTTIME: Sat Aug 08 17:41:07 EDT 2009
STATUS : ONLINE
LINEV : 122.0 Volts
LOADPCT : 2.0 Percent Load Capacity
BCHARGE : 100.0 Percent
TIMELEFT : 44.2 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
SENSE : Medium
LOTRANS : 088.0 Volts
HITRANS : 139.0 Volts
ALARMDEL : Always
BATTV : 13.5 Volts
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
STATFLAG : 0x07000008 Status Flag
MANDATE : 2006-01-16
SERIALNO : 3B0603X30613
BATTDATE : 2000-00-00
NOMINV : 120 Volts
NOMBATTV : 12.0 Volts
FIRMWARE : 825.B1.D USB FW:B1
APCMODEL : Back-UPS ES 650
END APC : Sat Aug 08 19:36:12 EDT 2009

I don't want to replace the battery if it's really a problem with the UPS itself. Besides it's almost cheaper to just buy a new ups instead of replacing this battery.

comments would be appreciated

Jeff.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • power
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 01:38 AM . Last Modified: ‎2024-03-22 03:12 AM

0 Likes
0
1039
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:38 AM . Last Modified: ‎2024-03-22 03:12 AM

This unit performs a Self test at start up and every 14 days automatically. If the unit fails the Self test, it will emit a constant tone with Power on and Replace Battery LEDs flashing alternatively.

Is the UPS powering on fine with normal load attached? or Is the UPS still making a constant beep with load attached after you power on it? Could you please let us know the light indication of the UPS when it is making the constant beep?

If it powers on fine with load attached, then I recommend you to stimulate a Power failure by unplugging it from the wall and check if it runs the equipment on battery as expected.

These information will help us to discover what is going on with the unit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Techie_apc
Techie_apc
Contributor

Posted: ‎2021-06-29 01:38 AM . Last Modified: ‎2024-03-22 03:12 AM

0 Likes
0
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 01:38 AM . Last Modified: ‎2024-03-22 03:12 AM

This unit performs a Self test at start up and every 14 days automatically. If the unit fails the Self test, it will emit a constant tone with Power on and Replace Battery LEDs flashing alternatively.

Is the UPS powering on fine with normal load attached? or Is the UPS still making a constant beep with load attached after you power on it? Could you please let us know the light indication of the UPS when it is making the constant beep?

If it powers on fine with load attached, then I recommend you to stimulate a Power failure by unplugging it from the wall and check if it runs the equipment on battery as expected.

These information will help us to discover what is going on with the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore