BE350R beeping and shut down computers

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE350R beeping and shut down computers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
3
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

BE350R beeping and shut down computers

Bought 5 UPS for my company around 3 weeks ago from COMPUSA
now 3 of them dont working
after power outage shut down computers and beeeeeeeeps with non stop and red light
here model number and serial
BE350R serial 3B0741X46632
BE350R serial 3B0741X42743
BE350R serial 3B0645X64613
Please advise
thank you

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • back-ups
  • battery
  • be350
  • beeping
  • defective
  • power
  • PowerChute
  • rebooting
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

I suggest you unplug your UPS's before all the PC's crash, if they haven't already. Andf get rid of the UPS's.

I bought one for myself and one for my friend's PC at work. Early this year the UPS started beeping in the early mornings; I thought it was a power outage. It happened occasionally. The next month my PC started rebooting. It took me a couple of weeks to realize it, because I wasn't paying much attention. But I didn't know what to do about it, and just let it go. Then it started rebooting as I was ON the PC, which got my attention - but I had no experience with anything like that and so didn't know what to do! I thought my PC was going bad. It never occurred to me that it was related to the UPS beeping! So I finally unplugged it all when the PC didn't recognize having a drive C, and a few weeks later bought a new Dell.

During the time I didn't have a PC my friend's PC at her job started rebooting! Eventually they got a technician to look at it and he told her the UPS had a SHORT and had ruined the company PC! That must be what happend to mine! What are the chances???? The CHANCES are that APC makes faulty equipment and then tries to rationalize it by giving everyone stupid tasks to do to trace down our problems!!!

Luckily my friend told me about it before I brought home my new Dell, so naturally I did not plug the UPS back in! But that doesn't make me feel less angry at APC or less guilty because I brought the UPS into her office...

The remark Il read about the "BE350R" being barely capably of handling a PC and monitor, blah blah blah is a poor excuse for poor equipment, because most people I think only use a PC and monitor. I would rather have mine hooked to a power strip than ever say anything nice about APC.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

pluged only one flat Dell LCD panel 19" and basic dell workstation nothing else
i was trying even conect just one LCD panel and i have same problem beeping and redlight after i unplug power from UPS
please help

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

What do you have plugged into them. The BE350R's are only capable of 165W, which is BARELY enough to cover a barebones PC and Monitor setup. It's possible that they were tripped to overload and need to be reset.

Have you tried starting them on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

I suggest you unplug your UPS's before all the PC's crash, if they haven't already. Andf get rid of the UPS's.

I bought one for myself and one for my friend's PC at work. Early this year the UPS started beeping in the early mornings; I thought it was a power outage. It happened occasionally. The next month my PC started rebooting. It took me a couple of weeks to realize it, because I wasn't paying much attention. But I didn't know what to do about it, and just let it go. Then it started rebooting as I was ON the PC, which got my attention - but I had no experience with anything like that and so didn't know what to do! I thought my PC was going bad. It never occurred to me that it was related to the UPS beeping! So I finally unplugged it all when the PC didn't recognize having a drive C, and a few weeks later bought a new Dell.

During the time I didn't have a PC my friend's PC at her job started rebooting! Eventually they got a technician to look at it and he told her the UPS had a SHORT and had ruined the company PC! That must be what happend to mine! What are the chances???? The CHANCES are that APC makes faulty equipment and then tries to rationalize it by giving everyone stupid tasks to do to trace down our problems!!!

Luckily my friend told me about it before I brought home my new Dell, so naturally I did not plug the UPS back in! But that doesn't make me feel less angry at APC or less guilty because I brought the UPS into her office...

The remark Il read about the "BE350R" being barely capably of handling a PC and monitor, blah blah blah is a poor excuse for poor equipment, because most people I think only use a PC and monitor. I would rather have mine hooked to a power strip than ever say anything nice about APC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore