Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Battery Test?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Battery Test?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
152
Techie_apc
Techie_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
3
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

Battery Test?

Hi,

Is there a way to test the battery on our UPSs? We are all on Mac.
Let me know if you need more info.

Thanks in advance.
Kelly

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • battery
  • mac
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

Hi,

With the BK300C, you'd have to do the test manually. This is the procedure:

Press the upper portion of the Power 1/0 switch and then switch "On" the equipment connected to the UPS. The Power 1/0 switch should be lit. Utility power is supplied to the equipment. Perform a simulated utility blackout test to confirm the UPS unit can switch from utility power to battery power and back again, without affecting equipment powered by the UPS. Connected equipment must be "On". Start the test by unplugging the UPS power cord.
+1. The UPS will then beep once every five seconds (or continuously) to remind you that your equipment is powered by a limited capacity power source.+
+2. Restore power to the UPS by reconnecting the UPS power cord. If the equipment operation was undisturbed throughout the testing, the system is operating properly.+

The other models listed will follow the every 14 day pattern. They will either have a replace battery LED flashing or power on/replace battery LED flashing at the same time. The 350's according to the manual will flash both lights and the 750 according to the manual will only flash the replace battery. There will also be constant tones. On the 500, Short beeping 2 times every 2 seconds for 1 minute repeated every 5 hours and Power On LED - flashing 2 times per second is what the manual states.

Essentially, you'd see some lights flashing and hear some beeping.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
BillP Leader
Leader

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

Hello,

What type of UPSs do you have? Most UPSs have a battery test that it runs automatically every 2 weeks (unless you have disabled it) or you can initiate it from the front panel of the UPS.

Let me know the type/exact model of UPS and I can tell you how to initiate a UPS self test (considered the battery test) but most likely, it does it every two weeks anyway.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

We have a variety of UPSs listed below:

- UPS 300 - BK300C
- UPS ES 350 - BE350U
- UPS ES 350 - BE350R
- UPS ES 500 - BE500U
- UPS ES 750 - BE750BB

If the battery runs a self-test automatically every 2 weeks, then what will it do to alert me when the battery is dead?

Thanks, Kelly

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

0 Likes
0
1429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:22 PM . Last Modified: ‎2024-03-26 12:31 AM

Hi,

With the BK300C, you'd have to do the test manually. This is the procedure:

Press the upper portion of the Power 1/0 switch and then switch "On" the equipment connected to the UPS. The Power 1/0 switch should be lit. Utility power is supplied to the equipment. Perform a simulated utility blackout test to confirm the UPS unit can switch from utility power to battery power and back again, without affecting equipment powered by the UPS. Connected equipment must be "On". Start the test by unplugging the UPS power cord.
+1. The UPS will then beep once every five seconds (or continuously) to remind you that your equipment is powered by a limited capacity power source.+
+2. Restore power to the UPS by reconnecting the UPS power cord. If the equipment operation was undisturbed throughout the testing, the system is operating properly.+

The other models listed will follow the every 14 day pattern. They will either have a replace battery LED flashing or power on/replace battery LED flashing at the same time. The 350's according to the manual will flash both lights and the 750 according to the manual will only flash the replace battery. There will also be constant tones. On the 500, Short beeping 2 times every 2 seconds for 1 minute repeated every 5 hours and Power On LED - flashing 2 times per second is what the manual states.

Essentially, you'd see some lights flashing and hear some beeping.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore