Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

BE 350 G will not stop beeping on battery mode

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BE 350 G will not stop beeping on battery mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
119
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

0 Likes
4
2080
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

BE 350 G will not stop beeping on battery mode

Hello

After reading the manual and searching on-line I can not solved this problem of my unit beeping.  4 beeps every 30 seconds, caused by overload. Everything since has been unplugged.

I have done the disconnect battery, hold the on button for 5 seconds, reconnect the battery and still when I plug it in and turn on the battery it still beeps.  When I unplug from power, it still beeps as expected since there is no power.  Plug it back in and turn on power, it starts beeping again.  When I turn off the battery, as expected the surge protections still works.  Would like to use the battery and surge protection outlets again...could someone please advise on how to get rid of these beeps.

Thank you 

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 350
  • beeps
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 01:38 AM . Last Modified: ‎2024-03-27 03:28 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:38 AM . Last Modified: ‎2024-03-27 03:28 AM

Yes, that was the first thing I tried.  But it didn't do anything, sits out 1/4".  Any other suggestions?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

Hi,

4 beeps every 30 seconds means your UPS is operating on battery mode - typically meaning wherever it is plugged into (the wall outlet?) is not providing good utility power and there is a potential power outage or power event. It has nothing to do with an overload besides the fact that you would not know an overload was happening until the UPS went to battery power. An overload would have a solid, constant tone and it would not provide power through the battery outlets. 

Let's start here. If you make sure the battery is securely connected, with no equipment plugged in to the battery back up outlets, and you know that your wall outlet is providing good power because a lamp or radio or similar works when connected to it, plug the UPS into the same wall outlet and turn it on and confirm what you hear/see.

If the UPS is operating on battery mode and there is no power outage or failure in your area, then we need to try and figure out why the UPS thinks there is an outage. You could try adjusting the sensitivity setting as it is possible the UPS "sees" something you don't like electrical noise.

Instructions on doing that are here -> http://www.apcmedia.com/salestools/SCON-89HJYJ/SCON-89HJYJ_R3_EN.pdf (refer to the bottom of page 1)

I hope this helps clarify. Let me know if you have any questions before you get started.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

Thank you for your reply.

I have an exact unit plugged into the same outlet and both have been running fine for years.  This morning I plugged in a heater and then that's when the unit when off after an hour of usage.  After unplugged the heater I can't get the unit to stop beeping even going to different outlets in the house and back to the same outlet where my other UPS is running fine without any signs of voltage outages or electrical noise.  I tried the sensitivity settings before posting but I can't get any other light but green; then when green is lit it start the 4 beeps per 30 seconds again.    

EDIT

Tried again now.  When I press the button it beeps.  When I hold the button down (10 Sec) its beeps and then gives a long tone.  Nothing else happens, no leds flashing to choose from, the light goes out.  If I press it a couple of times, then it turns green and starts the beep cycle again.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:37 AM . Last Modified: ‎2024-03-27 03:28 AM

Ok, let's check to see if the input circuit breaker popped. It can trip if excess current was drawn through the input, like from the heater. It would force the UPS to operate on battery. Refer to the photo below and let me know if you can push this breaker in. When it is not tripped, it usually sits out about 1/4" and if it is tripped, it is usually sticking out 1 and 1/4".

Qxu7z%2BrEXBaCNtIWJOFx6Q%3D%3D.jpegQxu7z%2BrEXBaCNtIWJOFx6Q%3D%3D.jpeg

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 01:38 AM . Last Modified: ‎2024-03-27 03:28 AM

0 Likes
0
2079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:38 AM . Last Modified: ‎2024-03-27 03:28 AM

Yes, that was the first thing I tried.  But it didn't do anything, sits out 1/4".  Any other suggestions?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore