BACK-UPS ES 550VA does not go to battery when power is lost.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • BACK-UPS ES 550VA does not go to battery when power is lost.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
2
722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

BACK-UPS ES 550VA does not go to battery when power is lost.

For some reason if power is lost my 550G-CN backup does not go to battery power. instead the computer shuts down instantly instead of the 4 minutes its supposed to last according to the powerchute program. Powerchute shows the battery is charged to 91%. Is this battery back toast?

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:16 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:16 AM . Last Modified: ‎2024-03-27 01:53 AM

Last year, our company purchased over 100 of these units to protect the PC's in two call centers.  Both call centers have backup diesel generators that will restore power within 5-10 seconds of a power failure, so we expected these APC units to keep the computers on until generator power kicked in. We don't have these backups overloaded, each has one small PC and two flat screen monitors plugged into them.

 

Between our two call centers, we've had a couple of power outages over this last year. The reports that started coming in were rows of computers suddenly losing power. I came to these forums today to see if anyone else was having issues with this model. We did some tests by walking down the rows and unplugging the APC from the wall and the APC does it's job and keeps the PC powered up.

 

I could see one or two units being bad, but not banks of them. I opened a ticket with APC and will update this post when/if i hear from them.

 

Denny

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

An immediate shutdown of the load attached to your UPS usually indicates a weak or worn out battery. If the unit is more than 3-5 years old, the battery is probably worn out.

You can replace the battery yourself if you wish to do so, it's quite safe and easy. A door on the underside of the unit slides open to reveal it. A really old battery might be somewhat swollen, in which case you might have to tap the unit to get it out. APC sells replacement batteries with warranty coverage or you can use a generic replacement (12V, 7 through 9AH) at your own risk.

If you decide to replace the entire UPS, I would recommend a larger capacity model. Four minutes may not be enough time if anything stalls or pauses when the computer shuts down, and that time will only decline as the battery wears out.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:16 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:16 AM . Last Modified: ‎2024-03-27 01:53 AM

Last year, our company purchased over 100 of these units to protect the PC's in two call centers.  Both call centers have backup diesel generators that will restore power within 5-10 seconds of a power failure, so we expected these APC units to keep the computers on until generator power kicked in. We don't have these backups overloaded, each has one small PC and two flat screen monitors plugged into them.

 

Between our two call centers, we've had a couple of power outages over this last year. The reports that started coming in were rows of computers suddenly losing power. I came to these forums today to see if anyone else was having issues with this model. We did some tests by walking down the rows and unplugging the APC from the wall and the APC does it's job and keeps the PC powered up.

 

I could see one or two units being bad, but not banks of them. I opened a ticket with APC and will update this post when/if i hear from them.

 

Denny

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore