APC BackUPS Pro BR1500GI does not meet the advertised specifications.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BackUPS Pro BR1500GI does not meet the advertised specifications.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:14 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
12
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:14 AM . Last Modified: ‎2024-03-27 01:54 AM

APC BackUPS Pro BR1500GI does not meet the advertised specifications.

Yesterday I went to my brother's home, he has a BackUPS Pro BR1500GI like me.
I put a 800W load on it (haswell-e + GTX980 Ti SLI clocked) and the UPS shutted down with F02 error, just like my BR1500GI.

We spent 800€ for two UPS that are advertised for 865W, this unit can't handle more than 770-780W without shutting down with strange error.

What APC has to say about this?
I would like to hear an official statement on this.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

Just to inform other people, I bought an Atlantis Land, I paid it half the price of the APC and it works like a charm.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:14 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:14 AM . Last Modified: ‎2024-03-27 01:54 AM

Davide,

How are you monitoring the load on the UPS to determine the wattage draw?

Is the error happening when the UPS switches to battery or when on AC?

If you are switching the UPS to battery how are you performing that? Unplugging from AC source?

What is the serial number of the BR1500?

Is the battery in the unit the original battery?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:14 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:14 AM . Last Modified: ‎2024-03-27 01:54 AM

I'm monitoring the load using the LCD present in the display and with a digital watt meter that I put on the AC socket.

The error happen when the UPS switches on battery. I discovered it when the UPS tried the self test when my PC was on and the PC immediately shutted down.

Yes, I unplug the AC source to test the UPS.

Serial Number: 3B1115X19770

The battery is new and genuine/original.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

Hi,

I tested similar units today. BR1500G (120 V) manufactured in 2012. I put a 856 watt loaded on the UPS (see screen shot). I ran a self-test and put the UPS on battery. In nether case did the UPS crash or give the F02 error. I also tested a BX1500G (120 V) from 2009 and it handled the load as expected. Both units had the original batteries. I was pleasantly surprised that the 2009 unit did not have an issue based on the battery age. Both units showed 3 minutes of run-time which matches our on-line graph. 

Note: I split the load between 2 outlets on the UPS. 600 watts on one and 256 on the other. Also, PowerChute warned me that the UPS would not sustain the load for 5 minutes which was the configured shut down threshold however it did power down the OS properly. 

I am looking for test information for units based on your serial number range. If I can find the information I will pass it on. 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

for what it worth in europe we use 220V not 120V.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

PS: can you tell me what you used to simulate a load of 865W?

we connect PSU to UPS not simulated pure load.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

Hi,

The load I used was static. Quantity 4 200 watt incandescent light bulbs, 1 40 watt incandescent light bulb, and 1 Dell 17 inch computer monitor. I used this load knowing that the bulbs would stay consistent through the test cycle.  

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

your test is much much easyer than a real load coming from an Active PFC Power Supply.
My Corsair AX860i has a PFC as all PSU in the world from ten years and PFC can create this kind of problem in cheap UPS.

APC UPS costs two times a "normal UPS", I didn't expected this behaviour from a unit of this cost.

PS: I tried with bulbs and I have no problem with bulbs. The problem comes when using a PC PSU. Do you test your UPS for PC use or for lighting? 
Really disappointed, I will spread this things on forums.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:54 AM

It's not so much the active PSU but the design of the power supply. Some of them exceed their power limit when the voltage drops. Exceeding the UPS specs will eventually cause it to shut off the output.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

If overloaded the UPS should give the overload error, not the F02 battery short error.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

On 2/15/2016 4:34 AM, Davide said:

If overloaded the UPS should give the overload error, not the F02 battery short error.

Hi Davide.  I think it's a matter of semantics.  I believe that the F02 error is not a battery short error but, rather, an output load "short" while on battery power.  The F02 error is much like an F01 (overload) error but taken to another level.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
1275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

Ok, in any case for the price of this unit I expected a little bit of "over engineering" other than "sub engineering".
I'm using a PSU that got a 10 out of 10 from jonny guru, no a cheap one.
the overshoot during outages must be small and at 810W (including 40W monitor) of load an UPS that is advertised for 865W should handle it.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

0 Likes
0
1276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:15 AM . Last Modified: ‎2024-03-27 01:53 AM

Just to inform other people, I bought an Atlantis Land, I paid it half the price of the APC and it works like a charm.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of