Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Automatic and explicit self test return opposite results

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Automatic and explicit self test return opposite results
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2150
Teken
Teken
150
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
5
1584
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

Automatic and explicit self test return opposite results

Hi all!

On one of our Back-UPS RS 800, running the self test from the OS returns WARNING, and the "Replace Battery" LED gets on.
But, if we turn the workstation off and then turn the UPS off and back on again, the automatic self test which runs on "power on" leaves the "Replace Battery" LED in its "off" status.

So which self test result is correct?
Should we change the battery or not?
The UPS is 2 1/2 years old.

Thanks, Richard

null

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:29 AM

0 Likes
0
1582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:29 AM

Hi all!

On one of our Back-UPS RS 800, running the self test from the OS returns WARNING, and the "Replace Battery" LED gets on.
But, if we turn the workstation off and then turn the UPS off and back on again, the automatic self test which runs on "power on" leaves the "Replace Battery" LED in its "off" status.

So which self test result is correct?
Should we change the battery or not?
The UPS is 2 1/2 years old.

Thanks, Richard

null

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

The Replace Battery LED was solid and yes, an audible alarm started.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:30 AM

Ok. It's most likely asking for a replacement battery. If you can do this, as part of troubleshooting, measure the battery voltage and it should be reading ~27V.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:30 AM

apcaccess (the command from apcupsd for Linux) shows

BATTV : 27.1 Volts

What does this value tell you?
We have another UPS, bought only about 2 months ago, showing the same voltage.

The other values shown by apcaccess are:

# apcaccess
APC : 001,043,1057
DATE : Wed May 05 18:43:25 CEST 2010
HOSTNAME : idefix
VERSION : 3.14.6 (16 May 2009) suse
UPSNAME : CHEUPS02
CABLE : USB Cable
MODEL : Back-UPS BR 800
UPSMODE : Stand Alone
STARTTIME: Wed May 05 16:58:18 CEST 2010
STATUS : ONLINE
LINEV : 228.0 Volts
LOADPCT : 26.0 Percent Load Capacity
BCHARGE : 094.0 Percent
TIMELEFT : 9.4 Minutes
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
OUTPUTV : 230.0 Volts
SENSE : Medium
DWAKE : 000 Seconds
DSHUTD : 000 Seconds
LOTRANS : 194.0 Volts
HITRANS : 264.0 Volts
RETPCT : 000.0 Percent
ITEMP : 29.2 C Internal
ALARMDEL : Always
BATTV : 27.1 Volts
LINEFREQ : 50.0 Hz
LASTXFER : No transfers since turnon
NUMXFERS : 0
TONBATT : 0 seconds
CUMONBATT: 0 seconds
XOFFBATT : N/A
SELFTEST : NO
STATFLAG : 0x07000008 Status Flag
SERIALNO : QB0707337059
BATTDATE : 2001-09-25
NOMOUTV : 230 Volts
NOMINV : 230 Volts
NOMBATTV : 24.0 Volts
NOMPOWER : 540 Watts
FIRMWARE : 9.o4 .I USB FW:o4
APCMODEL : Back-UPS BR 800
END APC : Wed May 05 18:43:57 CEST 2010

The battery charge value is at 94% because it went down today to 70% on one of my tests, it's charging now and it probably will go back to the 100% it had before.

Thanks,
Richard

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:29 AM

0 Likes
0
1582
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:29 AM

Hi,

1.
The reason why I suggested you to measure and see the battery voltage is because, sometimes it causes a replace battery LED to turn on detecting a weak battery voltage. But since, age is also considered to be one of the factors affecting the battery life, it's most likely wanting a new battery.

2.
During the self test the UPS will switch from online to on battery using ~25% of the battery charge, that's why it dropped to the level that you have specified.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:29 AM

0 Likes
0
1583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:22 AM . Last Modified: ‎2024-03-22 01:29 AM

Hi all!

On one of our Back-UPS RS 800, running the self test from the OS returns WARNING, and the "Replace Battery" LED gets on.
But, if we turn the workstation off and then turn the UPS off and back on again, the automatic self test which runs on "power on" leaves the "Replace Battery" LED in its "off" status.

So which self test result is correct?
Should we change the battery or not?
The UPS is 2 1/2 years old.

Thanks, Richard

null

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore