DLA1500i Smart-Ups battery/software reset.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • DLA1500i Smart-Ups battery/software reset.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
117
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
3
1440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

DLA1500i Smart-Ups battery/software reset.

Hi All.

I have a DLA1500i Smart-Ups 1500, which I cannot fault as it has served me well for the last three years.

My dilemma is that I am having trouble sourcing a new battery for the unit here in Dubai. The APC agent here tells me that it is an ‘old’ model and they are unable to source a genuine replacement battery but he can install a replacement that is commonly used in these ‘older’ models.

My question is this:
As the power chute software is working, I can stop the audio warning alarm telling me that the battery needs replacing. I have reset the date for the battery telling the unit it has a new battery hoping to reset the unit but the red led is still flashing telling me to replace the battery. The unit was purchased new three years ago and this was confirmed by the date of the battery installation information from the power chute software.
As I have one computer running on the unit there is only 7% draw at any one time. I have read that there is a way to ‘reset/fool’ the unit as if there was a new battery installed and to stop the audio alarm and flashing red led.

My question is therefore - HOW IS THIS DONE?
Obviously this is not ideal and a replacement battery is being sought but as a temporary work-around there must be away to reset the unit without replacing the battery. All my indications are that the battery is fine and this is a precautionary alarm indication only.

ANY IDEAS PLEASE.

Supplier Part #:DLA1500I
Supplier Parts Description:UPS 1500VA USB 230V
Product Serial #:AS0752110994
OS: XP
Business Edition Power Chute

Many thanks in advance.
Regards.
LakeTaupoHoliday.com

Message was edited by: LakeTaupoHoliday.com

Message was edited by: LakeTaupoHoliday.com

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

Hi All.

I have a DLA1500i Smart-Ups 1500, which I cannot fault as it has served me well for the last three years.

My dilemma is that I am having trouble sourcing a new battery for the unit here in Dubai. The APC agent here tells me that it is an ‘old’ model and they are unable to source a genuine replacement battery but he can install a replacement that is commonly used in these ‘older’ models.

My question is this:
As the power chute software is working, I can stop the audio warning alarm telling me that the battery needs replacing. I have reset the date for the battery telling the unit it has a new battery hoping to reset the unit but the red led is still flashing telling me to replace the battery. The unit was purchased new three years ago and this was confirmed by the date of the battery installation information from the power chute software.
As I have one computer running on the unit there is only 7% draw at any one time. I have read that there is a way to ‘reset/fool’ the unit as if there was a new battery installed and to stop the audio alarm and flashing red led.

My question is therefore - HOW IS THIS DONE?
Obviously this is not ideal and a replacement battery is being sought but as a temporary work-around there must be away to reset the unit without replacing the battery. All my indications are that the battery is fine and this is a precautionary alarm indication only.

ANY IDEAS PLEASE.

Supplier Part #:DLA1500I
Supplier Parts Description:UPS 1500VA USB 230V
Product Serial #:AS0752110994
OS: XP
Business Edition Power Chute

Many thanks in advance.
Regards.
LakeTaupoHoliday.com

Message was edited by: LakeTaupoHoliday.com

Message was edited by: LakeTaupoHoliday.com

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

Hi.

Thanks for your reply.

As mentioned, I am unable to source an APC battery for this unit here in Dubai. The reseller and service department information was from the official APC web site. If you have information where I can get the correct replacement battery here in the Middle East/Dubai I would be most grateful.

Failing a resolve to this situation, my only alternative is to get rid of the APC equipment and use a different manufacture. It’s unfortunate as I was under the impression that APC was a global company but it looks like I may not be able to have the required service support which I require after all.

Many regards.
LakeTaupoHoliday.com

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

I'd first try running a self-test on the unit with a greater load. Ideally you'll want more like a 20-25% load on the UPS to procure accurate self-test results. Since you only have a 7% load, that could be a false alarm, or it could be a legitimate battery issue. Granted, the batteries are expected to last 3-5 years so that may be the case.

The way to "trick" the UPS, like you're saying, isn't a recommended solution so APC isn't likely to provide you instructions on how to do so. I think a couple of people of posted here about it though, so maybe they can point you in the right direction.

If you legitimately need a replacement battery and are having trouble finding one locally... http://www.apc.com/tools/locator/index.cfm
I set the country to United Arab Emirates, left city/zip blank, selected "Miscellaneous Device" and checked the box for a country-wide search. Pulls up a bunch of APC certified partners, most of which are in Dubai.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

0 Likes
0
1441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-22 01:30 AM

Hi All.

I have a DLA1500i Smart-Ups 1500, which I cannot fault as it has served me well for the last three years.

My dilemma is that I am having trouble sourcing a new battery for the unit here in Dubai. The APC agent here tells me that it is an ‘old’ model and they are unable to source a genuine replacement battery but he can install a replacement that is commonly used in these ‘older’ models.

My question is this:
As the power chute software is working, I can stop the audio warning alarm telling me that the battery needs replacing. I have reset the date for the battery telling the unit it has a new battery hoping to reset the unit but the red led is still flashing telling me to replace the battery. The unit was purchased new three years ago and this was confirmed by the date of the battery installation information from the power chute software.
As I have one computer running on the unit there is only 7% draw at any one time. I have read that there is a way to ‘reset/fool’ the unit as if there was a new battery installed and to stop the audio alarm and flashing red led.

My question is therefore - HOW IS THIS DONE?
Obviously this is not ideal and a replacement battery is being sought but as a temporary work-around there must be away to reset the unit without replacing the battery. All my indications are that the battery is fine and this is a precautionary alarm indication only.

ANY IDEAS PLEASE.

Supplier Part #:DLA1500I
Supplier Parts Description:UPS 1500VA USB 230V
Product Serial #:AS0752110994
OS: XP
Business Edition Power Chute

Many thanks in advance.
Regards.
LakeTaupoHoliday.com

Message was edited by: LakeTaupoHoliday.com

Message was edited by: LakeTaupoHoliday.com

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore