Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Are the building wiring fault indicators ever known to be problematic?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Are the building wiring fault indicators ever known to be problematic?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:31 AM

1 Like
6
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:31 AM

Are the building wiring fault indicators ever known to be problematic?

I just purchased a new Back-UPS XS 900 to replace an ES 350 that served me well for over 3 years. The 350 was admittedly WAY too marginal and would have only given me around 3 mins. with the high powered dual CPU (not just dual core, dual CPU) full tower computer that runs 2 video displays. I have it set with a single desktop window, spanned across 2 monitors. Initially, the monitors were 17" CRT's. At that point, I likely wouldn't have even gotten 3 min. but what I did was to only plug the left side monitor (with the windows "Start" button) to try for a graceful shutdown, and the right side monitor plugged into just surge protect to try and maximize runtime on battery, while still permitting access to shutting down. I suppose I couldn't have been too "graceful" with only 3- mins.

Changing to (2) 19" LCD monitors was better. Still only had the left on battery back-up. This probably upped time to maybe 6 or 7 mins.

Anyway, battery in the ES 350 finally bit-the-dust, and when I saw a great deal on the XS 900, I decided to jump at it rather than put money into a new battery.

Now I'll probably have AT LEAST 30 mins. even with both LCD's on battery, maybe more. Definitely more if I leave it with only the left monitor on battery. Certainly, this will be a lot closer to what a reasonable back-up period SHOULD be.

But I've got a strange situation. The ES 350 did not have a building wiring fault indicator, so I never noticed anything. This new XS 900 does; and despite the fact that my house wiring has NEVER seemed to have ANY problem, no matter which outlet I try it in, the XS 900's wiring fault indicator is on constantly. There is no other trouble. Unit post's up just fine, leaving only solid green on light.

I even have a number of outlets that are GFI protected. The GFI's are fine. Yet even when plugged into a GFI, the fault indicator lights up.

Obviously I can continue to check things out. My house wiring, try it out in another house, etc. But before I get crazy, is it possible that the fault indicator circuit is the actual problem? Are these known to be problematic?

Part of the "great deal" on this unit I spoke of was a $15.00 rebate, so before I start cutting UPC symbols out of the box, I'm trying to cover all the angles on whether I should exchange this unit for a another.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ginbot86_apc
Lieutenant JG ginbot86_apc
Lieutenant JG

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

1 Like
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

(sorry for the late reply) If you go to a hardware store, you can find an outlet tester to see if there is a wiring fault (live/neutral mixed up, etc.). If it's fine, then the UPS is defective.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

No GFI will indicate an open ground wire for exemple. The GFI is constantly measuring what comes in and what comes out, I mean, if 10Amps are coming in, 10amps should be coming out via neutral wire - the neutral wire is the functional ground, not the safety ground, so when there is a fault that causes x amps in / x amps out to get unbalanced, the GFI makes the circuit breaker trip. This happens when someone accidentally touch the phase (hot) wire or when there is a current leakage because of numerous reasons, it can be a demaged wire touching something that grounds it or because of an internal applience fault making current being dumped to the the safety ground wire, this is considered to be a fault, a safety fault, so the circuit breaker should trip on this conditions. The GFI helps the circuit breaker trip a lot faster and at a minimum leakage current.

The building wiring fault LED might be indicating three things that you wouldn't notice otherwise. It indicates reverse polarity. Almost any applience if not all, can work with the polarities reversed, but this make the protection devices not work properly because the circuit breaker or fuse inside the device will be "protecting" the neutral wire instead of the hot. There are other issues regarding reversed polarities that I can't remember now, but the other thing this indicator might be telling is an open ground. Your outlet may not have a ground wire or its demaged. The third and last thing the indicator shows you is overloaded neutral wire, but this is not very likely within a house. If you correct the ground wire and the polarities and the wiring fault LED is still on, try unpplugging everthing inside your house. If the LED is still on, your UPS might have some kind of problem.

Either way, you should have an electrician check the electrical installation inside your house. Ask him to check the safety ground wire of every outlet and check for reversed polarities.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

0 Likes
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

to elborate on what rau said,

a site/building wiring fault indicates:

-missing or loose ground
-reversed polarities
-overloaded neutral wire

i am not too experienced with GFIs or anything but ive never heard of that causing a site wiring fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

0 Likes
0
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

GFIs are devices made to basically protect lives and not to notify one about faults on the safety ground wire in the outlets as some might believe.

100% of the current (amps) consumed by the appliances has to return to the neutral wire, if this ain't happening, it's because the current is going somewhere else than the neutral wire and it basically happens when:

- Someone is getting electrocuted - one becomes the "neutral wire" by closing (grounding) the circuit through its body.
- When the isolation of a wire is bad and the wiring touches a metalic part, which is capable of sending current to ground.
- Electronics, especially computers have a little bit of leakage current to the safety ground, usually not enough to make the most sensitive GFI break the circuit, but this might happen when many PCs are attached to that specifc circuit. If this happens, one less sensitive GFI can be chosen, but the sensitivity has to be carefully analysed before changing the GFI.

GFIs come in a variety of sensitivities, the most sensible ones are used to protect one from being electrocuted when accidently touches the hot (phase) pin of an electrical appliance cable when plugging or unplugging it. GFIs made to save one from being electrocuted are usually set to 30 miliamps of leakage current. If 30 miliamps is being leaked somehere else than the neutral wire, the circuit is instantaneously turned off by the GFI.

In Brazil we call it a Residual Difference Circuit Breaker or something close to it, (DDR in portuguese or DR for short or an IDR for GFI without a circuit breaker built-in). If there is a difference in the sum of what comes in and what comes out, the GFI breaks the circuit, that's basically it.

Message was edited by: rau

Reply

Link copied. Please paste this link to share this article on your social media post.

ginbot86_apc
Lieutenant JG ginbot86_apc
Lieutenant JG

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

1 Like
0
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:58 PM . Last Modified: ‎2024-03-22 04:30 AM

(sorry for the late reply) If you go to a hardware store, you can find an outlet tester to see if there is a wiring fault (live/neutral mixed up, etc.). If it's fine, then the UPS is defective.

Reply

Link copied. Please paste this link to share this article on your social media post.

dnchrist
Crewman dnchrist
Crewman

Posted: ‎2024-02-09 12:39 AM

1 Like
0
2024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-09 12:39 AM

I had the same issue with a  Back-UPS BX-1500G.  I checked it with a tester and found no problem.   I bought another one and have no problem.  The initial unit is defective.  (Don't believe everything you read in the manual.  It also told me my batteries were bad)

  • Tags:
  • Turned out to be a dust ball inside the unit on the sensor circuit board. BE CAREFUL!
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Spock Teken
Spock

Posted: ‎2024-02-09 08:52 AM

0 Likes
0
1996
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-09 08:52 AM

As another data point this can be caused by connecting the UPS to an extension cord / power bar that is missing the ground pin. This problem will sometimes appear when isolation transformers are modified to be used in *Tech Mode*.

 

Lastly, depending upon the UPS design topology a building wiring fault is caused by a Bootleg Ground. People used this method to fool GFCI testers and the potential home buyer. A more dangerous version is the reversed bootleg ground where the neutral and line is connected backwards to its intended posts.

 

As of this writing (2024) almost all cUL / ETL certified AFCI, GFCI devices check for proper grounding, wiring (line / neutral) before they will allow you to turn it on / reset. 

 

NOTE: A wiring fault may also be detected when an outlet is modified to separate the top and bottom outlets. Where the top and bottom are powered by two different breakers. This is especially dangerous if the breakers are on the opposite leg of the single split phase electrical system.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of