I've got a HP server connected to a APC Back-UPS CS650
It isn't a very high powered server, and the UPS is reporting that it's only at 21% of cpacity. Battery is showing as 100% charged.
When power is cut to the UPS, the server switches straight off (although the UPS front panel shows it has gone to battery and it beeps).
Does this suggest the UPS is faulty (it is brand new)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-22 12:21 AM
Double Post
Message was edited by: JonPro
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-22 12:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-22 12:21 AM
Also, if I pull the power to the UPS so it switches to battery, anything connected to it wont manually switch on.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-22 12:21 AM
Hello John,
It could be with the SineWave that the UPS produce
when it is On Battery. The Back-UPS family produces a step approximated
sinewave when it is on battery. Some load and or power supply does not
accept this kind of waveform. There are cases as well when the power
supply on the UPS is power factor corrected. See the kbase below:
Article Name:
Computers containing PFC (Power Factor Corrected) power supplies and their use with Back-UPS or Smart-UPS SC UPS.
Article Link: [http://nam-en.apc.com/app/answers/detail/a_id/8883/kw/drops%20loadHello]
Article Name: Equipment connected to a Back-UPS product turns off unexpectedly and/or reboots.
Article Link: http://nam-en.apc.com/app/answers/detail/a_id/20/kw/drops%20load
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-22 12:21 AM
Double Post
Message was edited by: JonPro
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.