AVR and Unit Sensitivity Operation for the BR1000G

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • AVR and Unit Sensitivity Operation for the BR1000G
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
2
1881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

AVR and Unit Sensitivity Operation for the BR1000G

I searched the knowledge base and the forums for the exact operation for both of these functions, and haven't found what I was looking for.  Beginning with the Unit Sensitivity function, if the A/C signal input into the UPS is "clean" and "stable" will the unit simple pass that voltage out of the UPS, for Ranges listed under that particular Sensitivity setting?  Secondly, is the AVR  Percentage (+/-11.2%) for both the "Boost" and "Trim" functions applied to every voltage listed in the ranges shown for the Automatic Voltage Regulation in the specifications?

The reason I ask these questions is to understand how the unit will operate under certain circumstances.  When the UPS is adjusted for "Sensitive Loads"/High sensitivity (88-136 Vac), and clean stable power between 88-93 volts is inputted into the UPS, what Voltages will be outputted?

This Voltage range 88-93 Vac, according to the Operators Manual, appears to be outside of the AVR voltage range but still within the Unit Sensitivity voltage range to pass the incoming voltage right through the UPS without AVR or switching to the battery.  The same thing does not seem to exist for the high end of the input Voltage range except when the UPS is adjusted for "Generator Sensitivity"/Low sensitivity.  When the Unit Sensitivity is set to "Default"/Medium or High sensitivity the high voltage limits are 139 Vac and 136 Vac which are lower then the listed high voltage limit of 141 Vac for the Automatic Voltage Regulation.  I take this to mean that all voltages from 126 -141 Vac will be "Trimmed" down and anything above that will cause the UPS the switch to the Battery.

Adjusting the UPS to Low sensitivity creates a gap of one Volt between the high limit of the  sensitivity mode and the AVR.  What happens when the AVR is "Trimming" down the input voltage of 141 Vac and then the input voltage moves up to 142 Vac?

This voltage gap between the AVR and unit Sensitivity exists on the lower end of the voltage range as well.  Looking at the AVR lower limit voltage of 94 Vac, when the AVR is "Boosting" up 94 Vac and then the clean stable input voltage moves down to 93 Vac what voltage is outputted from the UPS?

Thanks for any information on this.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • avr
  • br1000g
  • sensitivity
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
1881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

The best information I can offer is based solely on my own personal experience and experimentation. (A variable autotransformer, also called a Variac, is a handy thing to have.)

AVR for those Back-UPS models that have it usually only provides "one step" of adjustment in either direction (high or low voltage). If the line voltage exceeds the range over which AVR can compensate, the unit goes to battery and runs for as long as it can.

I tested a BX1000G (which only has an upward voltage adjustment capability) just now and regardless of the sensitivity setting, its only available AVR mode kicked in at 98-99 volts AC and shut off around 105 volts.

These units are technically considered "standby power supplies" and under normal circumstances, they only pass incoming power to the output (after filtering it, suppressing surges and removing noise of course). If your load requires more protection than these units can offer, APC does have some "dual conversion" models that run their inverters continually and use AC line power only to charge the battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
1881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

Bump.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

0 Likes
0
1882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:52 AM . Last Modified: ‎2024-03-27 01:25 AM

The best information I can offer is based solely on my own personal experience and experimentation. (A variable autotransformer, also called a Variac, is a handy thing to have.)

AVR for those Back-UPS models that have it usually only provides "one step" of adjustment in either direction (high or low voltage). If the line voltage exceeds the range over which AVR can compensate, the unit goes to battery and runs for as long as it can.

I tested a BX1000G (which only has an upward voltage adjustment capability) just now and regardless of the sensitivity setting, its only available AVR mode kicked in at 98-99 volts AC and shut off around 105 volts.

These units are technically considered "standby power supplies" and under normal circumstances, they only pass incoming power to the output (after filtering it, suppressing surges and removing noise of course). If your load requires more protection than these units can offer, APC does have some "dual conversion" models that run their inverters continually and use AC line power only to charge the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore