Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
APC ups to allow overload for a short duration
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:39 PM. Last Modified: 2024-03-2112:42 AM
APC ups to allow overload for a short duration
Hi,
I, long time ago, started a discussion about overload problem my old APC BACK-UPS RS 1500VA 230V. I have found out later, overload problem was not about faulty ups, but it was about my psu (of the computer).
Let me give you some figures.
lets say, We have an ups with a capacity of 900 watts
and lets say, computer draws 400-500 watts during normal operation.
With these figures, a "line interactive" ups should operate normally in blackout right?
I found out that this is true ONLY if computers psu power is lower than 900W.
I found out that if blackout happens, line-interactive ups takes couple of ms to intervene, after those miliseconds, psu draws as much power as it can to compensate its power loss for a very short time. (under 1 sec i guess). In this case, if psu's power exceeds ups power limit, then ups gives an overload error.
In my case, I have a 1200 watt psu, if i load everything on my rig, it draws 750 watts max. If i want to purchase a "line interactive" ups, according to my research, i must go above 1200W. Or i could buy an "online" ups 800-900 Watts of power.
My question and suggestion is this: In my country, some local ups brands have a feature,they allow their ups to be overloaded (during battery operations - blackout) for a very short time and they give numbers like : 110% overload for 10 secs 120% 5 secs 150% for 1 sec.
So i think APC dont do such a thing, but it would be great if APC implement a feature like that. Because It saves me the trouble to buy a 2000 Watt APC. Because in theory a 800-900 W APC should do the job (line interactive)