APC UTS10BI Generator power selection

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UTS10BI Generator power selection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:39 AM

0 Likes
3
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:39 AM

APC UTS10BI Generator power selection

Good day !!

Just bought the UTS10BI (not installed yet) along with the Honda EU6500iS generator. Reading the instruction manual (set-up), I became with a question concerning the initial setting of the generator.

Instruction for the backup 1 (generator) says to enter the power rating of the genetaror but do not mention if this is the "maximum" power rating or the "continuous" power rating.

Can you help me please ??  

Labels
  • Labels:
  • Universal Transfer Switch
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

0 Likes
0
685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

In my limited experience, you may need to experiment a bit.  I have the UTS6H and two EU2000i generators.  So, each 2000 is rated at 1600 continuous and 2000 for up to 30 minutes.  Running on one generator (not, repeat not, on ECO setting), if I set the power rating at anything above 1950, and regardless of actual load, the panel reboots continuously.   So, actual load 175 watts, panel reboots. 1950 or below, the panel doesn't reboot. 

Running at roughly 1200 watts continuously, with occasional spikes to 1750 watts lasting 10 to 15 seconds, the panel goes kinda nutso.  (I am taking those spikes at what the panel reports, and of course the actual short term spike may be different.  I observe the red overload light on the generator flashing for a fraction of a second.)  But it will repeatedly shut down and reactivate circuit 6 (set to delayable, TM, 5 on 5 off) every 10 seconds or so.  It shuts down circuit 2 (delayable, TM, 30 on 30 off).  Then it turns off up to about 4 circuits, turns a couple back on.

If I fire up the second generator and set the generator output at 3200 watts, all of that behavior disappears.  I think it may be that the speed of the throttle motor on the generator, the speed the panel cycles, and my delay/TM settings are all in a little feedback loop.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

0 Likes
0
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

Good day !!

Just bought the UTS10BI (not installed yet) along with the Honda EU6500iS generator. Reading the instruction manual (set-up), I became with a question concerning the initial setting of the generator.

Instruction for the backup 1 (generator) says to enter the power rating of the genetaror but do not mention if this is the "maximum" power rating or the "continuous" power rating.

Can you help me please ??  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

0 Likes
0
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

with an inverter style generator, I have gone with an "in between" number since the gen can run for a certain time a maximum.  My thinking was if I go into that range, it wouldn't be for more then 30 minutes, i.e. micro, toaster, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

0 Likes
0
686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 11:23 PM . Last Modified: ‎2024-03-20 12:38 AM

In my limited experience, you may need to experiment a bit.  I have the UTS6H and two EU2000i generators.  So, each 2000 is rated at 1600 continuous and 2000 for up to 30 minutes.  Running on one generator (not, repeat not, on ECO setting), if I set the power rating at anything above 1950, and regardless of actual load, the panel reboots continuously.   So, actual load 175 watts, panel reboots. 1950 or below, the panel doesn't reboot. 

Running at roughly 1200 watts continuously, with occasional spikes to 1750 watts lasting 10 to 15 seconds, the panel goes kinda nutso.  (I am taking those spikes at what the panel reports, and of course the actual short term spike may be different.  I observe the red overload light on the generator flashing for a fraction of a second.)  But it will repeatedly shut down and reactivate circuit 6 (set to delayable, TM, 5 on 5 off) every 10 seconds or so.  It shuts down circuit 2 (delayable, TM, 30 on 30 off).  Then it turns off up to about 4 circuits, turns a couple back on.

If I fire up the second generator and set the generator output at 3200 watts, all of that behavior disappears.  I think it may be that the speed of the throttle motor on the generator, the speed the panel cycles, and my delay/TM settings are all in a little feedback loop.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of