APC UPS switches to battery mode eventhough there is no power failure

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UPS switches to battery mode eventhough there is no power failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
6
9277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

APC UPS switches to battery mode eventhough there is no power failure

I am using APC UPS for last 3 years, now i have a strange problem that it turns on as usual and after few minutes it switches to battery mode and start beeping. it forces me to switch off my pc. can anybody help me how to solve this problem?

thanks in advance.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

Hi Kulot,

thanks for the reply. the unit details are as below:

BE 500Y-IN
Serial No: BB0732009601
INPUT 230 V-, 10/.6A 50Hz
output UPS OUTLETS 500VA:
SURG PROTECTED OUTLET:
230V~, 3.8A, 47-53Hz

and the problem is...when i switch on the UPS the light turns to green color and i am able to work on my pc. after 10 to 15 mins the light turns to orange color and start beeping. if i do not switch off the UPS, it automatically switches off. please let me know if you need any more information.

Thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

Hello there!

Thanks for the specs, I managed to pull up the pdf file of the manual for the unit. An amber LED on this unit can mean a number of ew things; the unit is either On battery, running low on battery, or running a selftest ( immediately after turning the unit on).!http://www.apc-forums.com/servlet/JiveServlet/download/21-6599-30176-1818/$5EEC8ECE01717CF8.jpg!

If you ask me I'd say that most probably the unit is running on battery due to inconsistencies in the input power (EMI/RFI, THD), or disturbance causing the battery to discharge. You might want to try to plug the unit into a different wall outlet/ different circuit to see if it does the same thing.




*I've attached the pdf of the manual, hope this helps!

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

Good day!

Can you include specifics of the APC unit like the part# , serial#, and what about the light indicators that are illuminated, or beeps that the unit makes. Are you using Powerchute Personal Edition? We need more information about the device or what it does so you can get the correct info.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

Hi Kulot,

thanks for the reply. the unit details are as below:

BE 500Y-IN
Serial No: BB0732009601
INPUT 230 V-, 10/.6A 50Hz
output UPS OUTLETS 500VA:
SURG PROTECTED OUTLET:
230V~, 3.8A, 47-53Hz

and the problem is...when i switch on the UPS the light turns to green color and i am able to work on my pc. after 10 to 15 mins the light turns to orange color and start beeping. if i do not switch off the UPS, it automatically switches off. please let me know if you need any more information.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:08 AM . Last Modified: ‎2024-03-21 05:45 AM

Hello there!

Thanks for the specs, I managed to pull up the pdf file of the manual for the unit. An amber LED on this unit can mean a number of ew things; the unit is either On battery, running low on battery, or running a selftest ( immediately after turning the unit on).!http://www.apc-forums.com/servlet/JiveServlet/download/21-6599-30176-1818/$5EEC8ECE01717CF8.jpg!

If you ask me I'd say that most probably the unit is running on battery due to inconsistencies in the input power (EMI/RFI, THD), or disturbance causing the battery to discharge. You might want to try to plug the unit into a different wall outlet/ different circuit to see if it does the same thing.




*I've attached the pdf of the manual, hope this helps!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

Hi Kulot,

Thanks for the help. I've already tried your suggestion but no success; however i'll do some more test and update you the result. thanks again.

Regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

You're most welcome Please post any updates if you can. Have a wonderful day!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

Hi, Sorry for the delay. The UPS is working fine now. the manual which u sent is helped...according to the instructions under transfer voltage and sensitivity adjustment, i selected LOW sensitivity setting(Green flashing)...it works fine. so the problem was with the voltage input in my house. thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

0 Likes
0
9270
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:09 AM . Last Modified: ‎2024-03-21 05:45 AM

Good day!

Can you include specifics of the APC unit like the part# , serial#, and what about the light indicators that are illuminated, or beeps that the unit makes. Are you using Powerchute Personal Edition? We need more information about the device or what it does so you can get the correct info.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore