Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

APC UPS XS-1500 Tripping a 20 amp breaker - What is the working load?

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UPS XS-1500 Tripping a 20 amp breaker - What is the working load?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
116
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
2
1220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

APC UPS XS-1500 Tripping a 20 amp breaker - What is the working load?

I have been using a UPS XS-1500 to protect an Apple Mac Pro Quad Core Desktop, that is acting as a workstation and data server for a home network. One year ago, the 20 amp dedicated circuit breaker for this system started to trip. I replaced the breaker. A year later after flawless operation, the replacement breaker is beginning to trip randomly at times when I am away from the Mac. Wiring is only 5 years old on the home. The only additional loads to the Mac Pro which draws 12 amps max on 120 volt service, comes from:
- Two Samsung 24" LCD monitors using about 55 to 80 watts each.
- Logitec remote Mouse
- Bose Companion 3 speaker system.
My question is this: With the above configuration, how much extra curent draw in amps does the XS-1500 draw? Does the XS-1500 have the capacity to absorb and protect the household (input) power source from any current draw down spikes that may occur from the equipment plugged into the APC? If not, does the XS -1500 add to the current draw down spike that occurs the the Mac Pro comes out of hibernation to survice a network or workstation need?
I could not get any input breaker capacity information on this unit. The newer APC UPS 1500VA LCD shows a max current input of 12A and a Input Breaker Capacity of 15A.
If this unit is similar to the UPS XS -1500 I am using, Would it make sense to assume that the 15A breaker limit covers what ever can be plugged into the APC. or do I need to add the Max Input Current load of the APC, 12A to the load of what is being plugged into the APC i.e. My Mac Pro and the other goodies?
Your thoughts and wisdom would be greatly appreciated on this series of questions.
Many Thanks,
Michael

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

I have been using a UPS XS-1500 to protect an Apple Mac Pro Quad Core Desktop, that is acting as a workstation and data server for a home network. One year ago, the 20 amp dedicated circuit breaker for this system started to trip. I replaced the breaker. A year later after flawless operation, the replacement breaker is beginning to trip randomly at times when I am away from the Mac. Wiring is only 5 years old on the home. The only additional loads to the Mac Pro which draws 12 amps max on 120 volt service, comes from:
- Two Samsung 24" LCD monitors using about 55 to 80 watts each.
- Logitec remote Mouse
- Bose Companion 3 speaker system.
My question is this: With the above configuration, how much extra curent draw in amps does the XS-1500 draw? Does the XS-1500 have the capacity to absorb and protect the household (input) power source from any current draw down spikes that may occur from the equipment plugged into the APC? If not, does the XS -1500 add to the current draw down spike that occurs the the Mac Pro comes out of hibernation to survice a network or workstation need?
I could not get any input breaker capacity information on this unit. The newer APC UPS 1500VA LCD shows a max current input of 12A and a Input Breaker Capacity of 15A.
If this unit is similar to the UPS XS -1500 I am using, Would it make sense to assume that the 15A breaker limit covers what ever can be plugged into the APC. or do I need to add the Max Input Current load of the APC, 12A to the load of what is being plugged into the APC i.e. My Mac Pro and the other goodies?
Your thoughts and wisdom would be greatly appreciated on this series of questions.
Many Thanks,
Michael

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

Erasmus,
Thank you for your thoughts on this. Very helpful! I am going to have the connection lugs in the breaker panel and outlet checked to make sure they are tight.
Best regards in the New Year,
Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

0 Likes
0
1221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:21 AM . Last Modified: ‎2024-03-22 02:37 AM

I have been using a UPS XS-1500 to protect an Apple Mac Pro Quad Core Desktop, that is acting as a workstation and data server for a home network. One year ago, the 20 amp dedicated circuit breaker for this system started to trip. I replaced the breaker. A year later after flawless operation, the replacement breaker is beginning to trip randomly at times when I am away from the Mac. Wiring is only 5 years old on the home. The only additional loads to the Mac Pro which draws 12 amps max on 120 volt service, comes from:
- Two Samsung 24" LCD monitors using about 55 to 80 watts each.
- Logitec remote Mouse
- Bose Companion 3 speaker system.
My question is this: With the above configuration, how much extra curent draw in amps does the XS-1500 draw? Does the XS-1500 have the capacity to absorb and protect the household (input) power source from any current draw down spikes that may occur from the equipment plugged into the APC? If not, does the XS -1500 add to the current draw down spike that occurs the the Mac Pro comes out of hibernation to survice a network or workstation need?
I could not get any input breaker capacity information on this unit. The newer APC UPS 1500VA LCD shows a max current input of 12A and a Input Breaker Capacity of 15A.
If this unit is similar to the UPS XS -1500 I am using, Would it make sense to assume that the 15A breaker limit covers what ever can be plugged into the APC. or do I need to add the Max Input Current load of the APC, 12A to the load of what is being plugged into the APC i.e. My Mac Pro and the other goodies?
Your thoughts and wisdom would be greatly appreciated on this series of questions.
Many Thanks,
Michael

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore