APC UPS BX-1100VA shuts down on its own

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC UPS BX-1100VA shuts down on its own
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS for Home and Office Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2022-05-22 10:32 PM

0 Likes
2
2987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-22 10:32 PM

APC UPS BX-1100VA shuts down on its own

I purchased a brand new UPS in October 2021 for my PS5 and TV. Has been working fine but I noticed that today morning the UPS shut off on its own. Both devices were switched off at the time. My apartment complex has a back-up generator which switches on within 10 seconds of a power cut. Today morning around 6AM there was a power cut which I'm assuming might have something to do with it but my area is prone to power cuts and I've never had issues before with the UPS. It has always switched from mains to back-up in the event of a power cut seamlessly and switched back to mains when the back-up generator switched on and power supply resumes 10 seconds later.

 

When I woke up, I tried to switch on the PS5 but noticed that it wouldn't switch on. I checked the UPS and noticed that the Power on/off light was off. I switched it back on and it blinked maybe 10-15 times and switched on. At the same time, the battery charging indicator switched on as well. Just to see if the battery continues to charge, I switched off the UPS again and this time the battery charging indicator was still on. The battery charging indicator remained on for may 20-25 minutes before the battery was charged completely. As of now, the UPS is functioning normally. I tried cutting the power from the mains and the UPS was working fine. 

 

This has happened before as well, probably 1.5 months ago. Same situation but last time there was a major fault with the power line in our apartment due to which power was cutting in and out regularly so I assumed that the UPS wasn't getting enough time to charge up and died because the battery ran out (no devices were switched on and powering the UPS when this happened).

 

Curious to know if something is up with the UPS. It's not even a year old yet. 

 

Thanks!

Labels
  • Labels:
  • Home & Office - UPS & Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
JonPro
Commander JonPro Commander
Commander

Posted: ‎2022-06-14 06:53 PM

0 Likes
1
2840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-14 06:53 PM

Hello @Anonymous user,

 

One possibility that I can see here is that the UPS has run on battery due to power issues.  It is possible that the generator kicks in but at that time, it might be supplying a distorted input to the UPS.

 

Unfortunately, with the information that we currently have, we wouldn't be able to fully diagnose the issue with the UPS.  I would recommend setting up PowerChute Personal Edition on a computer running a supported operating system and leaving it turned on for it to be able to record the power events that the UPS will encounter.

 

Please see the references below for your perusal.

  • PowerChute Personal Edition v3.1 
  • PowerChute Personal Edition Operating System Compatibility Chart 

 

I hope this helps.

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2022-06-14 09:35 PM

In response to JonPro
1 Like
0
2835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-06-14 09:35 PM

Thanks for you reply! I had an APC technician visit my apartment to examine the UPS. He ran the standard diagnostics and found nothing wrong. He did say that the UPS has a failsafe feature where it will sometimes shut down automatically when it detects highly irregular power supply to avoid damage to the UPS and the devices connected to it. This can sometimes happen during extreme weather conditions or when the source is providing fluctuating power which makes sense because the there was a thunderstorm going on when the UPS shut down. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore