Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

APC SMT 750i replace battery warning despite battery replacement

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • Re: APC SMT 750i replace battery warning despite battery replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
2151
Teken
Teken
156
voidstar_apc
voidstar_apc
83
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
rsdu
rsdu
Contributor

Posted: ‎2024-01-14 08:37 AM

0 Likes
7
20268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-14 08:37 AM

APC SMT 750i replace battery warning despite battery replacement

Hi there,

 

Before Christmas I bought a used APC SMT 750i with a "Replace Battery" warning. So I bought a new battery, installed it, ran a self-test, all fine. Ready to start Christmas, I left it without load.

 

When I returned after festive season, it showed a SOC of ~35% and a "Replace Battery" warning (including the beeping). I was unable to perform a new self test to reset the error because of low SOC. So I hooked the battery to an external charger and charged both packs. Then I reinstalled it (SOC shown ~70%) and was able to perform a new self test to inform the unit about the "swapped" battery. It successfully completed but the unit immeadtly after showed "Replace Battery" warning again.

 

Any ideas on how to further troubleshoot this? Do I have a faulty unit?

 

Many thanks for any ideas!

Marvin

Labels
  • Labels:
  • Home & Office - UPS & Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Teken
Champion

Posted: ‎2024-01-22 07:15 AM

In response to rsdu
0 Likes
0
20198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-22 07:15 AM

I did not see in your reply that once the battery was installed and the UPS was turned on. That you measured the battery to see (confirm) the UPS is indeed trying to recharge the cells. If the charger is working it should be above 28 VDC. 

 

Please do so and relay what you observe.

 


One thing I didn’t see mentioned is if you tried to connect the battery pack while the UPS was powered by AC Mains. Larger systems allow hot swapping the battery cartridge / pack while the UPS is operating. Normally when a pack is inserted the system will prompt to confirm a new cartridge is in place. This is followed by asking for the installation month / year. This can also be done using Power Chute Business / Home software ad well.

 

If you have the ability to tell the UPS a new battery pack is in place and also the installation date. This is important step to complete as this resets internal counters and also tells the UPS to use charging voltage / current (lookup tables) to manage charging the cells.

 

If the UPS has just positive / negative battery terminals you connect to. They are not hot swappable so use caution if you try to connect the pack while the unit is connected to AC mains. 

Let me know if your UPS has the ability to reset / tell the unit a new battery pack is in place. If it does great and reset / update that information.

 

The next step is to complete a battery calibration. This requires a 100% charged battery pack with a (minimum) 30% attached load. Unplug the unit from AC Mains and track how long it operates for. Let the UPS shut down and then remove any loads. Let it recharge and see what the UPS displays as SOC.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

rsdu
rsdu
Contributor

Posted: ‎2024-01-28 06:59 AM

0 Likes
2
20179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-28 06:59 AM

Again, Teken, many thanks for your reply!

I, indeed, missed part of your instructions and now performed the following based on your further instructions:

  1. Removed the battery pack and 230V.
  2. Reconnected 230V and started the USV. It indicated that the battery is missing.
  3. Reconnected the battery with the USV turned on.
  4. Confirmed the new battery and replacement date in the menu.
  5. Performed a calibration test -> Success! SOC at the end ~10%
  6. Waited for the SOC to raise to >70%.
  7. Performed a self-test -> Fail with "overvoltage on output" error
  8. Restarted the unit and performed the self-test again but with some load -> success!

With some load the unit now behaves as expected. Many thanks for your support!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Teken
Teken
Champion

Posted: ‎2024-01-17 11:58 AM

0 Likes
2
20236
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-17 11:58 AM

You can try the brain dead procedure which I have appended a link: https://www.apc.com/us/en/faqs/FA156611/

In the interim recharge the battery pack until they are 100% and let them sit for at least 24 hours. Measure the battery pack while at rest with nothing connected and relay what the resting voltage is.

 

For a single 12 volt battery it should be hovering around 13.6 ~ 13.8 VDC once charged. 

 

If the battery shows 12.80 - 12.90 VDC (which is considered full) only after 24 hours this indicates the cell are / is less than ideal. Reardless, once the battery pack is fully charged reconnect the pack into the UPS but leave the pack outside.

 

Take a multimeter (DMM) and measure the voltage once the UPS is connected to 120 VAC. Power on the UPS once it completes its POST (Self Test) use your multimeter and confirm the UPS is charging the battery pack. If say the battery pack is 12.XX / 24.XX prior to inserting the cells and it doesn't rise to say 14.XX / 28.XX there's something wrong with the charging circuit.

 

Two batteries in series is 24 volts DC, while floating it will be 27.XX, during charging it will be 28.XX VDC. As an aside what brand and (AH) are these batteries - how old?

Reply

Link copied. Please paste this link to share this article on your social media post.

rsdu
rsdu
Contributor

Posted: ‎2024-01-21 06:04 AM

In response to Teken
0 Likes
1
20218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-21 06:04 AM

Hi Teken,

 

Many thanks for taking the time to look into my issue 🙂

 

That's what I did and measured:

  1. Performed Brain Dead procedure as per given link.
  2. Loaded both batteries with external charger. Voltage 13,7V after 100% charge.
  3. Let both batteries rest for ~36hrs. Voltage 13,2V
  4. Insert batteries to UPS (left UPS off): Voltage 27,4V
  5. Turned on UPS
  6. Selftest completed successfully, but replace battery warning right after.
  7. UPS shows Battery Voltage of 27,3V and SOC of 32%.

The battery pack is from Battery Direct, model TBC48-BD1 with 7,0 Ah bought in December 2023.

I hope that helps in troubleshooting my issue. Many thanks for any advice!

 

Regards

Marvin

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-01-22 07:15 AM

In response to rsdu
0 Likes
0
20198
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-22 07:15 AM

I did not see in your reply that once the battery was installed and the UPS was turned on. That you measured the battery to see (confirm) the UPS is indeed trying to recharge the cells. If the charger is working it should be above 28 VDC. 

 

Please do so and relay what you observe.

 


One thing I didn’t see mentioned is if you tried to connect the battery pack while the UPS was powered by AC Mains. Larger systems allow hot swapping the battery cartridge / pack while the UPS is operating. Normally when a pack is inserted the system will prompt to confirm a new cartridge is in place. This is followed by asking for the installation month / year. This can also be done using Power Chute Business / Home software ad well.

 

If you have the ability to tell the UPS a new battery pack is in place and also the installation date. This is important step to complete as this resets internal counters and also tells the UPS to use charging voltage / current (lookup tables) to manage charging the cells.

 

If the UPS has just positive / negative battery terminals you connect to. They are not hot swappable so use caution if you try to connect the pack while the unit is connected to AC mains. 

Let me know if your UPS has the ability to reset / tell the unit a new battery pack is in place. If it does great and reset / update that information.

 

The next step is to complete a battery calibration. This requires a 100% charged battery pack with a (minimum) 30% attached load. Unplug the unit from AC Mains and track how long it operates for. Let the UPS shut down and then remove any loads. Let it recharge and see what the UPS displays as SOC.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

rsdu
rsdu
Contributor

Posted: ‎2024-01-28 06:59 AM

0 Likes
2
20179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-28 06:59 AM

Again, Teken, many thanks for your reply!

I, indeed, missed part of your instructions and now performed the following based on your further instructions:

  1. Removed the battery pack and 230V.
  2. Reconnected 230V and started the USV. It indicated that the battery is missing.
  3. Reconnected the battery with the USV turned on.
  4. Confirmed the new battery and replacement date in the menu.
  5. Performed a calibration test -> Success! SOC at the end ~10%
  6. Waited for the SOC to raise to >70%.
  7. Performed a self-test -> Fail with "overvoltage on output" error
  8. Restarted the unit and performed the self-test again but with some load -> success!

With some load the unit now behaves as expected. Many thanks for your support!

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Teken
Champion

Posted: ‎2024-01-29 05:38 AM

In response to rsdu
0 Likes
1
20177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 05:38 AM

That’s really great to hear! 👍 May I ask how much load was on the output when the over voltage error message occurred? Just wanted to clarify any informational steps I provided that may have led you astray.

 

Rock On . . . 🍺

Reply

Link copied. Please paste this link to share this article on your social media post.

rsdu
rsdu
Contributor

Posted: ‎2024-01-29 09:02 AM

In response to Teken
0 Likes
0
20157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 09:02 AM

There was no load connected when the over voltage error occured during the self-test.

 

Side observation: Current load is ~55W, as soon as I remove 230V and therewith force the unit to battery mode, the indicated load increases to ~230W. This still gives me about two minutes of runtime, which is fine for me. However, I expected a bit more ...

Reply

Link copied. Please paste this link to share this article on your social media post.

rsdu
rsdu
Contributor

Posted: ‎2024-02-25 08:48 AM

0 Likes
0
20095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-25 08:48 AM

For the folks googling this thread: There is a follow-up story https://community.se.com/t5/APC-UPS-for-Home-and-Office-Forum/APC-SMT-750i-replace-battery-warning-d...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore