APC RS 800 After new battery replacement there is continuous sound of flipping relays

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC RS 800 After new battery replacement there is continuous sound of flipping relays
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Kirk Teken
120
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
6
1782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

APC RS 800 After new battery replacement there is continuous sound of flipping relays

APC RS 800 After new battery replacement there is continuous sound of flipping relays, can anyone suggest some solution since the UPS in bed room its disturbs everyones sleep. the UPS is working as expected apart from the relay noise

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • after
  • apcrs800
  • battery
  • new
  • noise
  • relay
  • replacement
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

The things that can go bad are electrolytic Caps, yes end of life is also a major factor.. tracing them is a bit of headache

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

Hi Avinash, 

Can you please provide the model and serial number of this unit? It is located on a white sticker on the back or bottom of the UPS. Also, was the new battery you installed in the unit a genuine APC battery or a battery from a 3rd party vendor? 

Regards, 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

Thanks for your response, Model no is BR800-IN S/n is JB0646015002, by the way i have two BR800-IN units, The batteries which i have put is Exide chloride power 7AH-12V x2, These are the best i can find in this part of world, they have good service where i stay

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

Hi Avinash, 

Okay, I believe that is the issue you are having. We do not recommend using 3rd party batteries with our UPSs because we don't test our units with them and thus do not know how they will behave. I have seen customers use 3rd party batteries and they work fine, and I have seen them not work at all.

The APC replacement battery part number for this unit is the RBC32. They do sell this battery on Amazon if you are able to purchase from them. If not, you're unit is about 10 years old. Our UPSs have a typical lifespan of 7-10 years, so you may want to look into getting a replacement UPS. 

Regards, 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

Thanks for your reply Nicloe,

I discharged and charged the batteries once, my issue is resolved, and yes that unit is 10 years old and i guess it will give me service for few more years, i work for Exide hence i get batteries for way too less, and By the way im a Electronics engineer 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

Hello Avinash and Nicole,

 Retired USN data systems technician using APC UPS units in USN and at home for 36 years. First time encountering same situation as yours. I replaced battery with factory APC unit a year ago and relays started activating on frequent basis about 4 months ago between between AC/Battery. I will attempt your procedure of discharging battery to see if problem will rectify. I suspect though, either the unit suffers from inadequate design and or end of life point. I realize discrete components do not last forever for obvious reasons but it is disappointing nevertheless. I have high regard for APC and still prefer over any other brand. We will see about the outcome but as with so many products of this age, I believe the time for upgrade to a newer unit is probably on the near horizon. 

  • Tags:
  • 8
  • after
  • apc
  • battery
  • Engage
  • factory
  • frequently
  • later.
  • months
  • relays
  • replacing
  • rs800
  • with
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

0 Likes
0
1785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM

The things that can go bad are electrolytic Caps, yes end of life is also a major factor.. tracing them is a bit of headache

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore