APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Posted: 2021-06-28 04:51 AM . Last Modified: 2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:51 AM . Last Modified: 2024-03-27 01:26 AM
Hi,
Yesterday we had a powersurge at work. One computer with an APC backups cs 500 went full continuous tone, red replace battery light immediately. It didn't even TRY to provide power to the system. Uplugged everything out the back and still, continuous tone. Is that normal? Has anyone else had one of these units do that? It's like right when we needed it, it just totally gave up the ghost.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:51 AM . Last Modified: 2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:51 AM . Last Modified: 2024-03-27 01:26 AM
I would strongly suspect that the battery has failed, especially if the unit is more than five years old and using the original battery.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:51 AM . Last Modified: 2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 04:51 AM . Last Modified: 2024-03-27 01:26 AM
I would strongly suspect that the battery has failed, especially if the unit is more than five years old and using the original battery.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.