APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
APC RS 800 After new battery replacement there is continuous sound of flipping relays, can anyone suggest some solution since the UPS in bed room its disturbs everyones sleep. the UPS is working as expected apart from the relay noise
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
The things that can go bad are electrolytic Caps, yes end of life is also a major factor.. tracing them is a bit of headache
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Hi Avinash,
Can you please provide the model and serial number of this unit? It is located on a white sticker on the back or bottom of the UPS. Also, was the new battery you installed in the unit a genuine APC battery or a battery from a 3rd party vendor?
Regards,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Thanks for your response, Model no is BR800-IN S/n is JB0646015002, by the way i have two BR800-IN units, The batteries which i have put is Exide chloride power 7AH-12V x2, These are the best i can find in this part of world, they have good service where i stay
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Hi Avinash,
Okay, I believe that is the issue you are having. We do not recommend using 3rd party batteries with our UPSs because we don't test our units with them and thus do not know how they will behave. I have seen customers use 3rd party batteries and they work fine, and I have seen them not work at all.
The APC replacement battery part number for this unit is the RBC32. They do sell this battery on Amazon if you are able to purchase from them. If not, you're unit is about 10 years old. Our UPSs have a typical lifespan of 7-10 years, so you may want to look into getting a replacement UPS.
Regards,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Thanks for your reply Nicloe,
I discharged and charged the batteries once, my issue is resolved, and yes that unit is 10 years old and i guess it will give me service for few more years, i work for Exide hence i get batteries for way too less, and By the way im a Electronics engineer
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Hello Avinash and Nicole,
Retired USN data systems technician using APC UPS units in USN and at home for 36 years. First time encountering same situation as yours. I replaced battery with factory APC unit a year ago and relays started activating on frequent basis about 4 months ago between between AC/Battery. I will attempt your procedure of discharging battery to see if problem will rectify. I suspect though, either the unit suffers from inadequate design and or end of life point. I realize discrete components do not last forever for obvious reasons but it is disappointing nevertheless. I have high regard for APC and still prefer over any other brand. We will see about the outcome but as with so many products of this age, I believe the time for upgrade to a newer unit is probably on the near horizon.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2021-06-28 04:51 AM . Last Modified: ‎2024-03-27 01:26 AM
The things that can go bad are electrolytic Caps, yes end of life is also a major factor.. tracing them is a bit of headache
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.