APC ES 550 is clicking a lot

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC ES 550 is clicking a lot
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

0 Likes
7
3496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

APC ES 550 is clicking a lot

Hi folks,

New here basically just to check on this problem. I have an ES 550 and just a few days ago it started to click more and more.

I read the posts and messages that say it's probably normal but can someone confirm that? It seems to click more in the morning than evening but I don't think that makes a difference. All I have plugged into it is one laptop that I like to have running all the time.

Just want to make sure I'm not gonna come home one day and find out I have no home any longer. get it?

Thanks for the help

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:43 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:43 AM

Tex,

You can attempt to return the UPS to where you purchased it, and get another one. If you set that one to low and it's still clicking, that means there's excessive Harmonic Distortion (Electrical Noise) on the line feeding the UPS. It's possible that your older UPS had wider constraints, which Engineering may have found to result in more UPS failures due to passing through the noise, and therefore tightened the requirements on the new UPS's.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

Hello,

A clicking unit is a common problem where power isn't exactly "clean" and may contain a distorted sine wave. You should take action to correct this, as the unit is actually transferring back and forth to battery, which, overtime will cause the battery to weaken. To fix this situation, you need to adjust the sensitivity through our Powerchute software. Please see previous threads that discuss this further.

Referenced content removed

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

Thanks, I never used powerchute before because i keep the apc so far from my computer i didn't want another cord going across the room.

I changed it to medium sens though and hope that will fix it. I'll know 2nite or tomorrow when it notoriously has been waking up the last few days and sounded like chattering teeth.

Question, i don't need to leave it plugged into my computer right? I have unplugged it and moved it back to where i usually keep it.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Cap1_apc
Lt. Commander Cap1_apc
Lt. Commander

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

Correect, you do not need to keep Powerchute connected, you just need to change the setting, which is then saved to the unit.

I hope this helps!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

It does it less when the tv is off. Does that help?

All I have on this thing is a 27 inch tv, dvd player and tivo

Shouldn't come close to 550

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:44 AM

Just wanted to drop a line saying thanks, that definitely did help. I haven't heard a peep (or a click) in days.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:43 AM

0 Likes
0
3495
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:43 AM

I have the exact same unit and tried moving the sensitivity to "minimum" but it is still is clicking constantly. I never had this problem with my old 650V

Is there anything else I can try?

This unit isn't even 2 weeks old 😞

It just started this today.

Message was edited by: texmaster

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:43 AM

0 Likes
0
3496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 09:06 PM . Last Modified: β€Ž2024-03-26 12:43 AM

Tex,

You can attempt to return the UPS to where you purchased it, and get another one. If you set that one to low and it's still clicking, that means there's excessive Harmonic Distortion (Electrical Noise) on the line feeding the UPS. It's possible that your older UPS had wider constraints, which Engineering may have found to result in more UPS failures due to passing through the noise, and therefore tightened the requirements on the new UPS's.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore