APC Back-UPS ES500 shuts down itself and releases beeping sound.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC Back-UPS ES500 shuts down itself and releases beeping sound.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
6
7677
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

APC Back-UPS ES500 shuts down itself and releases beeping sound.

Hey guys,
Ive been using this model for almost 2-3 years now and this is the first major problem ive faced. I was playing my Ps3 earlier (ps3 and tv connected to the Back UPS) and suddenly it just switched off and released a beeping sound until i press and hold the power button,to turn it off. I tried again and the same thing happened for another 2 times. Ive afraid to use it again because the automatic shut downs may damage my Ps3. I didn't even know there was a special battery in it (yes i know,what an idiot,lol) but based on some searching i did,it could possibly be a problem with the battery. Am i right? Any idea whats wrong?
Thanks in advance πŸ™‚

This is the number on the sticker behind the unit :BE500r-AS

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

Thank you for your reply Clarkson.

This is how it happened the first time and subsequently :
I was playing the ps3 for not more than 15 mins when the Back-UPS (herein after referred to as the unit) suddenly just turned off. My tv went off and ps3 went off at the same time. It happened as if there was a black out. Immediately after the unit 'crashed',there was a loud permanent beep. No pattern to the beeping,just a long beep until i press the power button to turn it off.

As far as i remember,there was no light on the LED when it turned off and started beeping. Even after i press the power button,there was no light but im guessing thats because the act of pressing the button was to turn it off.

I dont really think there was any power fluctuations but something weird happened earlier when i decided to just try it on. I turned on the unit,and this starts the TV as its directly connected. I left the tv on standby with the unit on for 2 hours and everything was fine. Then i turned on the ps3 after 2 hrs,and within 5 mins the unit crashed. That should really give an idea of whats wrong,significantly narrowed down now πŸ™‚

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7674
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

Paltimes,

Do you have any software installed on your PC? Aside from the beeping sound and flashing green LED, did the UPS dropped its load? Have you tried doing a pull plug test to see if the UPS would have sufficient run time to support the equipment connected on the battery side? Based from your description, it appears that the UPS is showing the Low Battery Warning condition. It could have been caused by the UPS switching to On Battery state due to power problems such as over/under voltage, black out, frequency out of range and total harmonic distortion.

Low Battery Warning: While Operating On-Battery, the UPS has reached the default 2 minute Low Battery condition and will soon shutdown. The 2 minute Low Battery condition can be adjusted through PowerChute Personal Edition to give the customer more of a warning of impending shutdown. This graceful shutdown will occur automatically if the APC management software is being used.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

Thank you for your reply Clarkson.

This is how it happened the first time and subsequently :
I was playing the ps3 for not more than 15 mins when the Back-UPS (herein after referred to as the unit) suddenly just turned off. My tv went off and ps3 went off at the same time. It happened as if there was a black out. Immediately after the unit 'crashed',there was a loud permanent beep. No pattern to the beeping,just a long beep until i press the power button to turn it off.

As far as i remember,there was no light on the LED when it turned off and started beeping. Even after i press the power button,there was no light but im guessing thats because the act of pressing the button was to turn it off.

I dont really think there was any power fluctuations but something weird happened earlier when i decided to just try it on. I turned on the unit,and this starts the TV as its directly connected. I left the tv on standby with the unit on for 2 hours and everything was fine. Then i turned on the ps3 after 2 hrs,and within 5 mins the unit crashed. That should really give an idea of whats wrong,significantly narrowed down now πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

No it was the same setup for 6 months. I dont even remove those plugs,so it basically just happened out of the blue. Any idea whats wrong or what i should do? :S

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:35 AM . Last Modified: β€Ž2024-03-21 11:03 PM

Oh okay,but the problem is,im here in Malaysia and i dont think there's any APC 'HQ' here. I bought the unit when i was buying my computer. The shop sells computer equipment and such and i saw this product and decided to get it. I dont think i even have the box/receipt... Is there anything i could do in this situation :S?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

Great! Thanks a lot for the link clarkson. Ill give it a go when i get back home. You've been very helpful,i really appreciate it πŸ™‚

If i find out anything new,ill post it here πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

My Back-UPS ES500 releases beeping sound with green light flashing. What's wrong it it and what do I do?

MODEL BE500R-PH
SERIAL NUMBER 5B0710T18354

It's five years old, and this is the first time it did what it does. Any suggestions will be appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

0 Likes
0
7675
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 05:36 AM . Last Modified: β€Ž2024-03-21 11:03 PM

Paltimes,

Do you have any software installed on your PC? Aside from the beeping sound and flashing green LED, did the UPS dropped its load? Have you tried doing a pull plug test to see if the UPS would have sufficient run time to support the equipment connected on the battery side? Based from your description, it appears that the UPS is showing the Low Battery Warning condition. It could have been caused by the UPS switching to On Battery state due to power problems such as over/under voltage, black out, frequency out of range and total harmonic distortion.

Low Battery Warning: While Operating On-Battery, the UPS has reached the default 2 minute Low Battery condition and will soon shutdown. The 2 minute Low Battery condition can be adjusted through PowerChute Personal Edition to give the customer more of a warning of impending shutdown. This graceful shutdown will occur automatically if the APC management software is being used.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore