APC BX600C-IN 600VA, 230V Back UPS is TRIPPING MCB sometimes.

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BX600C-IN 600VA, 230V Back UPS is TRIPPING MCB sometimes.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

0 Likes
7
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

APC BX600C-IN 600VA, 230V Back UPS is TRIPPING MCB sometimes.

I'm from India and i have this UPS : https://www.apc.com/shop/in/en/products/APC-Back-UPS-600-230V-without-auto-shutdown-software-India/P...

Few weeks ago my UPS was flashing red and green alternate signal which points towards a bad battery or low power.(Please confirm me from its online manual, I got the warning only once) but Yes, its old.

but since then once a week as soon as i turn on the UPS(and the ups starts charging) my MCB trips. I fix the MCB and it runs for another week until it trips again. 

My friend told me this might be because the UPS is pulling more current to charge the already discharged old battery? The MCB for my computer's socket(plus 2 fans and a light) is rated at 6A, 1000w. Can the UPS pull more than 6 Amps when charging the discharged battery? Can that be the reason?

-Much Thanks

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

Hi Sam,

We do not have a guide on how to open the UPS as the battery in the BX600C-IN is not user replaceable.

Regards,

Tom

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

Hi Sam,

I cant see the UPS pulling more than 6A by itself, however if the UPS is suffering an internal battery short, it may be enough along with the additional circuit load to trip the MCB. Batteries can develop sulfite crystals from being continuously charged and discharged over long periods of time. This would result in the bad battery indication you have received. I would expect that you would be continuing to receive the same indications, so I'm not sure why that has stopped. I would recommend replacing the UPS, as attempting to charge a bad or shorted battery can cause overheating and is not recommended.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

On 11/9/2018 10:27 PM, Secret said:

Hi Sam,

I cant see the UPS pulling more than 6A by itself, however if the UPS is suffering an internal battery short, it may be enough along with the additional circuit load to trip the MCB. Batteries can develop sulfite crystals from being continuously charged and discharged over long periods of time. This would result in the bad battery indication you have received. I would expect that you would be continuing to receive the same indications, so I'm not sure why that has stopped. I would recommend replacing the UPS, as attempting to charge a bad or shorted battery can cause overheating and is not recommended.

Secret Squirrel

Hii. Thanks for your reply!! And yes i have got the battery signal only once a month ago. And the MCB trips only once a week or so and it happens only when immediately switching on the ups. On subsequent try, it runs fine. Although the pc can still run on battery for 3 mins.

I don't really know what to do. Replace the ups or battery? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

0 Likes
0
1465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

I recommend battery replacement. I believe that would be the APCRBC110.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:12 AM

On , said:

I recommend battery replacement. I believe that would be the APCRBC110.

Thanks.

I called APC and they said they don't make official batteries in India. Instead suggested me to go for Exide batteries from 3rd party..do you have any information on that? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

Hi Sam,

I'm sorry I don't. I will say however, exide is the largest selling battery company in India. If you were to reach out to a reseller of computer electronics, they should be able to point you in the right direction.

Secret Squirrel

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

Hi again. I'm considering changing the battery myself. Can you please tell me where can I get a guide to open my UPS BX600C-IN? Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

0 Likes
0
1466
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:33 AM . Last Modified: ‎2024-03-26 04:11 AM

Hi Sam,

We do not have a guide on how to open the UPS as the battery in the BX600C-IN is not user replaceable.

Regards,

Tom

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of