APC BR800I fails on line, runs on battery, blinks (Back UPS RS 800 VA)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BR800I fails on line, runs on battery, blinks (Back UPS RS 800 VA)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
100
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Guschtel
Crewman Guschtel
Crewman

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2024-03-21 05:00 AM

0 Likes
3
1479
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2024-03-21 05:00 AM

APC BR800I fails on line, runs on battery, blinks (Back UPS RS 800 VA)

Hello,

yesterday my APC BR800 I started to show unusual behaviour.
My apcupsd (i'm using linux) send me an email with the notice of a power failure (although no power failure occured), then another notice that power was restored and then back and forth the same thing with 1 minute delay.
Today the thing failed completely and my computers were all shut down.
The Status in the Emails is ONBATT and Battery charge is at 100%.

So today i turned it off and on again, didn't help.
I removed all cables from the UPS, turned it on then the line led blinks, after a few seconds the UPS switches to battery, then starts switching back and so on so forth.
I've made a video (17megs) to show what it does:
[Link to the video/pictures|http://algo.informatik.uni-freiburg.de/~hermann/temp/deleteme/apc/]
http://algo.informatik.uni-freiburg.de/~hermann/temp/deleteme/apc/

Is the UPS broken? I assume its not a battery problem since when the battery needed to be changed i got another message and i think the UPS should work regardless of the battery state, if power is on line.

Any help would really be appreciated.

regards
Christoph Hermann

Message was edited by: Guschtel

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • apc
  • back-ups
  • battery
  • beeping
  • blinking
  • br800i
  • failure
  • hardware
  • power
  • sensivity
  • solution
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2025-05-30 12:50 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2025-05-30 12:50 AM

Hi Christoph,

The way I see it is that your UPS performs the standard self-test when you first turn the unit on and gets stuck on Online and On Battery. It appears that the UPS is not seeing a good input voltage or frequency. If you have the APC PowerChute Personal Edition installed on a machine, I recommend that you use that first to adjust the sensitivity of the unit. We might need to adjust it to a lower setting.

If you do not have PCPE installed, then we would use the manual method to adjust it. You could use this Video KBase to adjust it first.

[Video: BX/BR Manual Adjustment for Sensitivity]

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2025-05-30 12:50 AM

0 Likes
0
1478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2025-05-30 12:50 AM

Hi Christoph,

The way I see it is that your UPS performs the standard self-test when you first turn the unit on and gets stuck on Online and On Battery. It appears that the UPS is not seeing a good input voltage or frequency. If you have the APC PowerChute Personal Edition installed on a machine, I recommend that you use that first to adjust the sensitivity of the unit. We might need to adjust it to a lower setting.

If you do not have PCPE installed, then we would use the manual method to adjust it. You could use this Video KBase to adjust it first.

[Video: BX/BR Manual Adjustment for Sensitivity]

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Guschtel
Crewman Guschtel
Crewman

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2024-03-21 05:00 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2024-03-21 05:00 AM

Thanks for the hint!
Setting the sensivity to low did indeed help. Before i tried setting it to medium which did not help.
And since apprently nothing changed regarding my electric circuits, i'm still wondering why the APC suddenly changed its behaviour.

So far, so good. My APC is back online again with battery at 100%, load 40%.

If anything else happens i'll post back here.

Thanks for the support!

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2024-03-21 05:00 AM

0 Likes
0
1477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:19 AM . Last Modified: ‎2024-03-21 05:00 AM

You are welcome Christoph.

There's a possibility that the problem is the harmonic distortion that is being fed into the UPS. If you have high powered devices, motor, laser printers and the like can sometimes introduce what do we call as dirty power into your circuit. If the waveform or frequency becomes to distorted the UPS sees this as a bad power and could sometimes damage your load.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of