Posted: 2024-05-08 12:06 PM
APC BR1600SI with PSU Corsair HX1500
Good evening.
Recently i bought an APC BR1600SI and i will use it with the PSU Corsair HX1500.
The problem it's that this PSU have the "big" power cord, while the BR1600SI use the "small" power cord one.
Do i need an particolar cable for it? I'm also wondering how to connect the router in this UPS.
- Labels:
-
Back-UPS & Surge Protectors
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-10 01:35 PM
Hi The BR1600SI uses a C13/C14 outlet while the PSU Corsair HX1500. Uses a C19/C20 plug from what I saw
meaning this unit is designed for a higher amp rating typically the C13/C14 s rated at 10 Amps while the C19/C20 is rated for 16 amps if you are in the US as per electrical code you should only use 80% of the capacity to avoid overheating of the conductors. The power supply is at 1500 watts at 230 (1500 /230 = 6.52 amps) it will only run a maximum of 6.5 amps way below the capacity of a C19 or even a C13 plug you can get a C19 to C14 cable to use for the power supply
https://www.apc.com/us/en/product/AP9878/power-cord-c19-to-c14-2-0m/?Chat_CSC_ID=a3080010
Also please note that the UPS BR1600SI can only support a load of 960 watts on battery so if you are maximizing the UPS capability you may need to get a bigger UPS
See Rated Power in watts on the UPS product page