APC BE700G-GR (Need Help)

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • APC BE700G-GR (Need Help)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
125
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

0 Likes
9
1644
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

APC BE700G-GR (Need Help)

Hi all,

I just bought an APC BE700G-GR, and its great but the thing is:

I let the UPS charge till its battery capacity hit 100%, the estimated battery was 22 minutes, but when i tried to test the UPS, it showed me that the estimated battery time was 15 minutes only, and when i charge it again to 100%, it shows me that the battery estimated time is 22 again, does this mean that battery is dying, although its brand new (the whole device)?

Is the estimated battery time about running my PC in idle conditions only, or is it also 15 minutes when running my PC on load?

lastly, i want to ask if i had to leave it on constantly. i prefer powering it off after shutting down my PC (not from the wall socket, just the On/Off button), but i heard that this would lower the life of the battery, so is that true?

one last thing when i power off the UPS and turn it on again, it shows me that the estimated battery time is 40 minutes, but when i test it, it goes to 15 or 20 minutes again.

Thank You


Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

When the UPS is running online (versus on battery), the runtime is an estimate. When it runs on battery, it is constantly calculating the runtime so this tends to be a more accurate number. A few instances of this is almost like a runtime calibration as well.

If this is concerning, you can unplug your UPS (and data cable if attached) and let it run until the UPS turns off by itself - so maybe do this with something other than your computer. When it charges back up, this should be a little more accurate as it is a calibration.

Anyway, this behavior sounds normal.

The runtime estimate is the estimate based on the current load percentage. It should change based on load.

A UPS is intended to remain on all the time. Every time you turn it on, it does a self test so doing this every day could put unnecessary stress on the battery after a year or two of every day transferring to battery. The self test normally runs once every two weeks if you leave it on all the time. I would just leave the UPS on all the time and turn your computer off for the evening unless you have a very specific reason for turning it off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

While I agree with what you're saying, a Back UPS is not super advanced unfortunately so it does not constantly report that it is on battery. So since PCPE missed the initial on battery transfer before you turned your computer on, it had to wait for the low battery shutdown signal which would be the next step on the shutdown timeline. Thus, it did not work as you (or I would expect).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

Hi all,

I just bought an APC BE700G-GR, and its great but the thing is:

I let the UPS charge till its battery capacity hit 100%, the estimated battery was 22 minutes, but when i tried to test the UPS, it showed me that the estimated battery time was 15 minutes only, and when i charge it again to 100%, it shows me that the battery estimated time is 22 again, does this mean that battery is dying, although its brand new (the whole device)?

Is the estimated battery time about running my PC in idle conditions only, or is it also 15 minutes when running my PC on load?

lastly, i want to ask if i had to leave it on constantly. i prefer powering it off after shutting down my PC (not from the wall socket, just the On/Off button), but i heard that this would lower the life of the battery, so is that true?

one last thing when i power off the UPS and turn it on again, it shows me that the estimated battery time is 40 minutes, but when i test it, it goes to 15 or 20 minutes again.

Thank You


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

When the UPS is running online (versus on battery), the runtime is an estimate. When it runs on battery, it is constantly calculating the runtime so this tends to be a more accurate number. A few instances of this is almost like a runtime calibration as well.

If this is concerning, you can unplug your UPS (and data cable if attached) and let it run until the UPS turns off by itself - so maybe do this with something other than your computer. When it charges back up, this should be a little more accurate as it is a calibration.

Anyway, this behavior sounds normal.

The runtime estimate is the estimate based on the current load percentage. It should change based on load.

A UPS is intended to remain on all the time. Every time you turn it on, it does a self test so doing this every day could put unnecessary stress on the battery after a year or two of every day transferring to battery. The self test normally runs once every two weeks if you leave it on all the time. I would just leave the UPS on all the time and turn your computer off for the evening unless you have a very specific reason for turning it off.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:58 AM

i'm really sorry about this disturbance but i wanted to ask one more question:

I had a Real blackout today and the UPS worked perfectly On Idle And Load, and i shut down my PC Completely after the battery hit 70%, but i didnt power off the UPS or remove it from the wall socket. When i opened my PC again after 1 hour or so (the blackout lasted 20 minutes), i found out that the battery was at 55% and charging (it was discharging although i powered off my whole PC), do i have to power off/remove the UPS from the wall socket after i shut down my PC in a blackout or should i leave it as i did?

By The Way, are there any Extended Batteries for my UPS?

I Know that my questions are alot, but this will be the last time and i'm really sorry for the disturbance.


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:57 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:57 AM

We're here to help!

How did you configure your PowerChute software. There are two options - keep your computer on as long as possible or preserve battery power. This will either cause the UPS to discharge almost until no battery capacity is left or shutdown your computer shortly after the power outage and then turn the UPS off to preserve charge.

Did you manually power off your PC?

The UPS is designed to remain on all of the time so I'd recommend you configure your PowerChute software with one of the options I mentioned above depending on what you want to do.

Lastly, only some of the BX and BR type UPSs offer extended battery packs - none of the BE series like you have do.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:57 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:10 PM . Last Modified: ‎2024-03-21 12:57 AM

I configured it to keep it as long as possible. If i choose the other option (Preserve Battery After An Amount Of Time), Will it stop the discharge of the battery after i shut down my PC? (I Found Out that the discharge would stop at 25% after the blackout)

Yes, I manually power off my PC after the blackout.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

this whole set up is designed to do a graceful shutdown for you. When the PC is off and PowerChute is no longer running, the UPS is going to do a 'low battery shutdown' which means it will run as long as possible and then turn off. So if you want it to preserve battery power, let it do its thing and gracefully shutdown the computer for you and preserve battery power.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

Ok, Thank You Very Much Angela.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:11 PM . Last Modified: ‎2024-03-21 12:57 AM

You're welcome smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore