A possible way of dealing with failures of the Energy Management feature

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • A possible way of dealing with failures of the Energy Management feature
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2150
Teken
Kirk Teken
127
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Start a Topic
Solved
azbruno_apc
Ensign azbruno_apc
Ensign

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

0 Likes
4
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

A possible way of dealing with failures of the Energy Management feature

I recently got a BE750G and could not get the Energy Management to work. The basic problem is that as long as the feature is enabled on the device, there is no power to the controlled outlets, regardless of what is in the master and what it's on/off state is and what all the settings are. I got a replacement unit and it too fails. I've seen from the forums that it is not just me experiencing this.

A thought occurred to me today. Since PowerChute PE can turn the Energy Management feature on or off in the UPS unit, is there a way to programmatically do this through a Windows script or other means. What I would like to do is have something I can schedule to run automatically when Windows is booted to disable the feature, thus powering the controlled outlets. And when Windows shuts down, I'd like to programmatically enable the feature, thus cutting power to the controlled outlets.

Hopefully someone at APC could get this done. As a former programmer, I would expect it to be rather trivial.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

Hi,

Why not disable the feature using the master switch on the UPS? There are 2 switches on the ES750. 1 is the power / Off - On switch and the other is the Master enable switch. If you disable the Master outlet using the switch the controlled outlets will power up and stay powered up no mater what is plugged into the Master outlet.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

I don't have an answer, but that sounds like a great idea. Here's where I would look:

Many UPS features can be controlled via the documented USB Power Device HID though I suspect master-control would be a proprietary usage. Maybe wireshark and usbpcap would help. Additionally, some forum members have had success controlling UPS settings through PowerChute registry entries. Lastly, I would take a look at apcupsd.

Reply

Link copied. Please paste this link to share this article on your social media post.

azbruno_apc
Ensign azbruno_apc
Ensign

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

Thanks for the suggestions, voidstar.

I had completely uninstalled PowerChute and installed apcupsd, just to see if that would help. But I couldn't find any way through that to turn the feature on or off so I'm back to PowerChute. I'll look at the other things you mentioned.

My years as a programmer would tell me that for someone who's worked on PowerChute it should be a one day job to create such a program. All the needed code is already in PowerChute. No UI is needed, just a simple command, e.g. ...

C:> apcgreen -[on|off]

While it could be more complex to set up the delay times and thresholds, that can be done easily through PCPE as they needn't change.

Actually, a programmatic method as I'm suggesting would be valuable for another reason. My PC goes to sleep a number of times during the day as I'm not always working on it. If I plug in my LaserJet to a controlled outlet, then each time the PC came out of sleep mode, the LaserJet would run through its power-up cycle before going into its own low energy mode. Better to leave things plugged in and idle until the PC is really shuts down.

Anyone?

Reply

Link copied. Please paste this link to share this article on your social media post.

azbruno_apc
Ensign azbruno_apc
Ensign

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

0 Likes
0
1122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

I recently got a BE750G and could not get the Energy Management to work. The basic problem is that as long as the feature is enabled on the device, there is no power to the controlled outlets, regardless of what is in the master and what it's on/off state is and what all the settings are. I got a replacement unit and it too fails. I've seen from the forums that it is not just me experiencing this.

A thought occurred to me today. Since PowerChute PE can turn the Energy Management feature on or off in the UPS unit, is there a way to programmatically do this through a Windows script or other means. What I would like to do is have something I can schedule to run automatically when Windows is booted to disable the feature, thus powering the controlled outlets. And when Windows shuts down, I'd like to programmatically enable the feature, thus cutting power to the controlled outlets.

Hopefully someone at APC could get this done. As a former programmer, I would expect it to be rather trivial.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

0 Likes
0
1123
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:45 PM . Last Modified: ‎2024-03-20 03:53 AM

Hi,

Why not disable the feature using the master switch on the UPS? There are 2 switches on the ES750. 1 is the power / Off - On switch and the other is the Master enable switch. If you disable the Master outlet using the switch the controlled outlets will power up and stay powered up no mater what is plugged into the Master outlet.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore