Hi, I am new and here is the first post.
I have kill-a-watt and I checked both APC UPSes I have
First, an APC Back-UPS ES 550
I plug the kill-a-watt into ES 550 and I plug a 40W incandescent lamp in it. the ES is plugged into a GFCI outlet. I push the TEST button on the GFCI, the power goes out and now I run on battery. I use my Mac laptop to monitor the charge left in the battery and when I get to 50% I stop and restore the power. All this time, the kill-a-watt showed 115V and 59.9 Hz.
I do the same thing with a APC Back-UPS XS 800. Before I cut the power off, the kill-a-watt shows 59.9 Hz and 125V. I trip the GFCI, the lamp is now running on battery, the kill-a-watt shows 115V but the frequency jumps anywhere between 30 and 40 Hz. Occasionally I see a 42Hz, a 28Hz, but most of the time it's 32-35-36 Hz in that range. I can actually see the lamp flickering. Of course, because this is a much higher capacity UPS, it takes forever to run down the battery to 50%, (50 minutes with the 40W lamp) and eventually I stop after about 30 minutes at 70% charge. I restore the power, and now the kill-a-watt goes back to 59.9 Hz.
So is the second unit functioning properly? can the 30-40 Hz power damage something? I was about to hook this up to my Plasma TV (average 200 W, max stated in the manual 540 W but I never saw this on the kill-a-watt).
thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:01 AM . Last Modified: 2024-03-22 02:18 AM
The output from that unit should definitely be 60hz, or within a range of roughly +/- 1hz when on battery. A frequency of 30-40hz is not normal and should not be used to power any attached load. I would call into tech. support @ 1-800-800-4272 and let them assist you with a few more troubleshooting tests, then investigate whether you are in warranty to provide an RMA.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 03:01 AM . Last Modified: 2024-03-22 02:18 AM
The output from that unit should definitely be 60hz, or within a range of roughly +/- 1hz when on battery. A frequency of 30-40hz is not normal and should not be used to power any attached load. I would call into tech. support @ 1-800-800-4272 and let them assist you with a few more troubleshooting tests, then investigate whether you are in warranty to provide an RMA.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.