3 1-year old BackUPS XS 900's showing overload with nothing plugged in

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • 3 1-year old BackUPS XS 900's showing overload with nothing plugged in
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
99
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
5
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

3 1-year old BackUPS XS 900's showing overload with nothing plugged in

I purchased four APC BackUPS units approx. a year ago, three XS 900 units and a single XS 1500. The three XS 900 units, in rapid succession, began squealing a continuous beep with the red "Overload" light lit on each. One was simply plugged in with nothing attached to it and presumably turned off. The other two had a computer and monitor on it, nothing else, the other had a clock, lamp, and set of speakers....not exactly a huge draw in wattage.

What I have noticed is that a fan inside each unit seems to be dying....making horrible noises when running and mostly quits turning, which I believe leads to the overload alarm, which is more likely an overheating of the heatsinks the fans are attached to.

Thankfully, the 1500VA unit has yet to malfunction.....

So, anyone else having a problem with this particular unit? Too heavy to send back in for warranty service.......

Message was edited by: Beanie54

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • 900
  • alarm
  • beeping
  • cooling
  • fan
  • overload
  • xs
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

I had the same problem, after unit on for about ten minutes with no load, overload lights and beeping noise. Since the unit was out of warranty, I opened the case, turned it on and noticed the cooling fan did not operate. I purchased one from www.allelectronics.com for $1.75, installed it, and everything works fine.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

I purchased four APC BackUPS units approx. a year ago, three XS 900 units and a single XS 1500. The three XS 900 units, in rapid succession, began squealing a continuous beep with the red "Overload" light lit on each. One was simply plugged in with nothing attached to it and presumably turned off. The other two had a computer and monitor on it, nothing else, the other had a clock, lamp, and set of speakers....not exactly a huge draw in wattage.

What I have noticed is that a fan inside each unit seems to be dying....making horrible noises when running and mostly quits turning, which I believe leads to the overload alarm, which is more likely an overheating of the heatsinks the fans are attached to.

Thankfully, the 1500VA unit has yet to malfunction.....

So, anyone else having a problem with this particular unit? Too heavy to send back in for warranty service.......

Message was edited by: Beanie54

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

I had the same symptoms -- noisy fan when working, no fan and squealing alarm when not. I just replaced the fan and the UPS seems to be doing well now. See my comment in [this thread|http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/2218/apc-be325r-alarm-doesn-...] for more information.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

I recently inherited a three year old XS-900r with dead batteries. I replaced the batteries and the UPS has been working great for about three weeks...until early this morning. I was woken up by the alarm accompanied by an overload light. I unplugged everything from the unit, powered it down, and unplugged it. It has been doing this repeatedly all day and I've noticed the fan is loud and working overtime. I'm assuming the fan is to blame after reading this thread. The next time the unit sounds the overload alarm, I'll check to hear if the fan is working. If not, where can I find a suitable replacement fan?

Thanks,

- J.

P.S. Unfortunately, my UPS is only ten days out of warranty, according to APC's website. Any chance they'd replace the unit for me as a measure of goodwill? We have four APC UPSes in our house, so we're clearly loyal customers.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
0
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

I have exactly the same symptoms on exactly the same unit. It just woke me up at midnight, squealing. There was no power outage, and it wasn't overloaded. I unplugged all load from the unit, turned it off/on. In a few minutes it started doing it again -- with no load plugged into it.

The fan was making a faint noise, but not loud. My diagnosis is the same as Beanie54 -- failed fan leading to overheating leading to overload alarm and UPS shutdown. My XS900 is more than two years old, so I'll just replace it.

It sounds like a widespread problem. I see other posters have reported similar problems: http://forums.apc.com/spaces/4/back-ups-surge-protectors/forums/general/2218/apc-be325r-alarm-doesn-...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

0 Likes
0
1319
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 02:24 AM . Last Modified: ‎2024-03-22 02:34 AM

I had the same problem, after unit on for about ten minutes with no load, overload lights and beeping noise. Since the unit was out of warranty, I opened the case, turned it on and noticed the cooling fan did not operate. I purchased one from www.allelectronics.com for $1.75, installed it, and everything works fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now