2 UPS's in daisy-chain

APC UPS for Home and Office Forum

Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS for Home and Office Forum
  • 2 UPS's in daisy-chain
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
2151
Teken
Spock Teken
101
voidstar_apc
Janeway voidstar_apc
83
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS for Home and Office Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

0 Likes
4
2492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

2 UPS's in daisy-chain

Hi,

All we know that we will get know that our UPS battery has worn out during power failure incident.

What if reduce the negative risk of this failure while connecting 2 UPS's in daisy-chain ?

APC FAQ gives some comments on that

http://www.apc.com/solutions/display.cfm?id=59BFAC22-5056-AE36-FE722E8CC1311295&ISOCountryCode=gr

The argumentation that it will not double the capacity is acceptable, but please give your comment if it will work in the situation one of UPS battery is worn out.

Thank you for your comments in advance.

Labels
  • Labels:
  • Back-UPS & Surge Protectors
  • Tags:
  • daisy-chain
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

0 Likes
0
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

If you are talking about a common neutral, and separate phases into each input, then yes most will allow that. It's not remotely ideal as it means the ATS must make a slower transfer process to avoid arcing and consequential relay welding, but yes.

I think the thing that has been missed about a series UPS configuration is the glitch that causes the UPS to switch over will switch both units simultaneously. If your downstream UPS has a fault, you'll lose your load anyway before it has a chance to switch back as its input is supplied by the upstream UPS. It's just not practical for a whole host of reasons. An ATS is a really nice solution as it will sit and drain the primary UPS while the secondary one idles. It'll then switch over and go until the secondary dies. Not as efficient as properly sizing a UPS, but it'll work.

I use an AP7721 here. I have an SUA3000 on the primary input, and either a spare UPS or commonly just a straight plug to the wall on the secondary input. This allows me to take the UPS out of service for maintenance without losing the load. A second hand AP7721 was much cheaper (and far more versatile) than an external bypass switch.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

0 Likes
0
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

Hello:

While your scenario may theoretically work in some cases, it is not the way a UPS is designed to work and is not something we can recommend.  As the knowledge base you linked states, we don't recommend daisy chaining UPS's in any situation.  As you mentioned, the UPS should notify you in time if the battery has gone bad.  

If your load is critical enough that you think redundant UPS's are necessary, then perhaps you might want to look into an Automatic Transfer Switch.  With two compatible UPS's, you can plug each input of the transfer switch into a different UPS and the device will switch over in the event that one powers off.  

You can find information on these devices here:  http://www.apc.com/shop/us/en/categories/power-distribution/transfer-switches/rack-mount-transfer-sw....  Just make sure you confirm compatibility with the UPS's you are using.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

0 Likes
0
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

Dear Caleb,

re

>> As you mentioned, the UPS should notify you in time if the battery has gone bad.

It seems that I have failed to express myself, I wanted to say that "we can not know in advance that the battery is bad, UPS will never tell this in advance". I used to learn not single time, UPS pass testing and calibration and after a month, during the power supply incident, UPS does not help because of battery is dead.

However your suggestion to look at ATS (which is new for me) answers to my question how to manage this scenario.

Thank you indeed.

Arvidas

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

0 Likes
0
2491
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

I wonder if ATS can be fed with two separate 230V phases of 380 V AC power supply, if it is designed to do so ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

0 Likes
0
2492
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 05:36 AM . Last Modified: ‎2024-03-27 12:52 AM

If you are talking about a common neutral, and separate phases into each input, then yes most will allow that. It's not remotely ideal as it means the ATS must make a slower transfer process to avoid arcing and consequential relay welding, but yes.

I think the thing that has been missed about a series UPS configuration is the glitch that causes the UPS to switch over will switch both units simultaneously. If your downstream UPS has a fault, you'll lose your load anyway before it has a chance to switch back as its input is supplied by the upstream UPS. It's just not practical for a whole host of reasons. An ATS is a really nice solution as it will sit and drain the primary UPS while the secondary one idles. It'll then switch over and go until the secondary dies. Not as efficient as properly sizing a UPS, but it'll work.

I use an AP7721 here. I have an SUA3000 on the primary input, and either a spare UPS or commonly just a straight plug to the wall on the secondary input. This allows me to take the UPS out of service for maintenance without losing the load. A second hand AP7721 was much cheaper (and far more versatile) than an external bypass switch.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of