Dear All,
we have serveral SmartUPS-2200 and SmartUPS-3000 with SNMP Managemnet Adapters.
To shutdown the Servers if Power fails I have to install PowerChute Software on each Server which should go shutdown if power fails - Please correct me if I'm wrong!
But when to use which Software
Power Chute Business Edition?
Power Chute Personal Edition?
Power Chute Network shutdown???
I am confused - Plese help!
best regards
Werner
Posted: 2021-07-01 03:16 AM
This reply was originally posted by Angela on APC forums on 5/23/2013
For Smart UPS with Network Management Cards (AP9606, AP9617/18/19, AP9630/31), you'll need PowerChute Network Shutdown.
For Smart UPS with NO SmartSlot accessories installed (incase anyone is wondering) and for USB or serial communications, use PowerChute Business Edition.