Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Symmetra LX FAULT
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0103:16 AM. Last Modified: 2024-03-0511:00 PM
Do you know the model of card? Is it AP9619 or AP9631? I am betting AP9619. You can verify in the web UI under Administration->General->About assuming you have recent firmware.
This means that someone has configured the dry contacts options on the management card. Do you use dry contacts to signal something externally, such as an alarm beacon, a fan, a PLC, etc? If not, then this is not a concern. I imagine you'd know if it was a concern by what the device attached to your dry contacts is doing.
More often than not, I see these blindly configured and the user not understanding what they are for. When I ask about dry contacts, I am talking about the blue keystone jack on the front faceplate of the management card itself. Most likely there is an active condition on the card or UPS causing it to change to an abnormal state. If no dry contacts are in use, then it doesn't matter.
Within your web interface, I'd go to the Environment tab and look at output relay sections and see what's configured in there. You can also remove all of the configurations in this screen too.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0103:16 AM. Last Modified: 2024-03-0511:00 PM
Do you know the model of card? Is it AP9619 or AP9631? I am betting AP9619. You can verify in the web UI under Administration->General->About assuming you have recent firmware.
This means that someone has configured the dry contacts options on the management card. Do you use dry contacts to signal something externally, such as an alarm beacon, a fan, a PLC, etc? If not, then this is not a concern. I imagine you'd know if it was a concern by what the device attached to your dry contacts is doing.
More often than not, I see these blindly configured and the user not understanding what they are for. When I ask about dry contacts, I am talking about the blue keystone jack on the front faceplate of the management card itself. Most likely there is an active condition on the card or UPS causing it to change to an abnormal state. If no dry contacts are in use, then it doesn't matter.
Within your web interface, I'd go to the Environment tab and look at output relay sections and see what's configured in there. You can also remove all of the configurations in this screen too.