Back UPS and PowerChute Personal 3.0.2 -Computer does not come back on after power is restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Back UPS and PowerChute Personal 3.0.2 -Computer does not come back on after power is restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
7
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

Back UPS and PowerChute Personal 3.0.2 -Computer does not come back on after power is restored

Hello,

I have a new Back UPS 550G and have been testing it with the PowerChute Personal 3.0.2 Software, and when I pull the plug, every thing works as expected, i.e., the balloon pops up, 1 minute later the Hibernate dialog comes up, and 10 seconds after that, the machine hibernates. One minute after that, the monitor loses power (standby light goes out). If I plug it back in, the monitor returns to stand by (no signal) but the computer does NOTHING - unless I set the BIOS "AC Back" setting to "Full-On." Meaning that anytime the computer has been without power, e.g. unplugged or the power supply rocker switch turned off so I can work on it, as soon as power is restored, it starts up. This is an inconvenient side effect.

Is this the way it is supposed to work, or is there another way to get the USB port to wake it up after power has been withdrawn.

I have a GIGABYTE GA-H55M-USB3 Motherboard with an Intel Core I3 processor, and Award Bios, the latest offered by Gigabyte, and Windows 7 Professional 64 bit.

Any ideas?

Thank you,

Jim

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • back-ups
  • PowerChute
  • windows
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

Hopefully Bill will also add any additional comments if he has them now smile and you're welcome!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

Yes, I believe that is the issue here based on article ID FA159550 in our knowledge base (http://www.apc.com/site/support/index.cfm/faq/)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

Angela,

Thank you for your reply. The BIOS "Power-Back-On" setting does seem to be involved here. I found that if I set it to "Memory" (last known awake state). I could put the computer to sleep (which is hybrid sleep and also does a hibernate), and if I toggled the rocker switch on the power supply off then on, it would come roaring back to life, of course having lost the RAM and needing to resume from the hibernate file on disk. Sadly, when I sent it directly to "Hibernate" (without going to Sleep first), Removing and then restoring power did not bring it back to life until I hit the power button.

I cannot find a way to set the PowerChute software to simply put a computer to sleep (knowing that "hybrid sleep" would also trigger a hibernation save), which would allow the computer to come on when power is restored. Can the action labelled "Shut down" in PowerChute be changed?

I'll also be pursuing the BIOS side of things to see if there's a way to get it to wake up from S4 (hibernate) on return of power.

Thank you for your help.

Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:16 AM . Last Modified: ‎2024-03-05 11:00 PM

Hi Jim,

Thanks for the further information and clarification on your situation. I just relayed this to Bill P. (my PowerChute loving co-worker wink) as he handles support for this product regularly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

Hi Angela,

Should I be posting to a different group? Calling Tech Support? I never did hear from Bill P, but I have been doing some experimenting and learning.

Clearly, the only way the computer can "know" that it needs to start up (unattended) is when it sees power again.

  • I can set the BIOS to turn the system on immediately whenever AC Power is "restored," which really means any time I plug into a wall outlet (in addition to power restoration after failure). This is a  bit awkward.
  • I can set it to turn on immediately whenever power is restored and it was in state S3 (sleep) before power went out. (on the face of it this seems odd but see below Hybrid sleep).
  • I cannot get it to turn on if it was left in state S4 (hibernation). This is where Powerchute leaves it.

OK you may be wondering, what is the point of putting a computer to sleep just before withdrawing power from it? Sleep depends on power. The answer is that Windows uses (unless the feature is disabled) Hybrid Sleep: It goes through all the motion of getting ready to hibernate, i.e., writes out the hiberfil.sys and saves the state, but then Sleeps, i.e., enters S3. The idea is that most of the time you don't lose power and just wake from S3 sleep,, but it you do, the computer can just resume from  hibernation. The key is it never enters S4.

Re-applying power cannot restart it from S4. Now if I could only get Powerchute to simply put it to sleep (S3), Windows will take care of the rest.

Best,

Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

Well, I gave the feedback to Bill to give to our product management team but I don't know if any changes will happen overnight unfortunately..but any future revisions would be where we could make modifications to this process. Sorry if I did not make that clear previously.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

That's OK. I guess I wasn't clear on whether this issue fell into the category of there's something I'm missing or you can't do that with the software the way it is now. It's not a big deal. It's a very small fraction of the time that I would really need my computer to start up by itself anyway instead of waiting for me to turn it on.

Thank you for your help.

Best,

Jim

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 03:17 AM . Last Modified: ‎2024-03-05 11:00 PM

Hopefully Bill will also add any additional comments if he has them now smile and you're welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore