when use which Power chute Edition?

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
wesiewert_apc
Crewman
Crewman
0 Likes
1
137

when use which Power chute Edition?

This was originally posted on APC forums on 5/23/2013



Dear All,

we have serveral SmartUPS-2200 and SmartUPS-3000 with SNMP Managemnet Adapters.

To shutdown the Servers if Power fails I have to install PowerChute Software on each Server which should go shutdown if power fails - Please correct me if I'm wrong! 

But when to use which Software

Power Chute Business Edition?

Power Chute Personal Edition?

Power Chute Network shutdown???

I am confused - Plese help!

best regards

Werner


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
137

Re: when use which Power chute Edition?

This reply was originally posted by Angela on APC forums on 5/23/2013


For Smart UPS with Network Management Cards (AP9606, AP9617/18/19, AP9630/31), you'll need PowerChute Network Shutdown.

For Smart UPS with NO SmartSlot accessories installed (incase anyone is wondering) and for USB or serial communications, use PowerChute Business Edition.

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
138

Re: when use which Power chute Edition?

This reply was originally posted by Angela on APC forums on 5/23/2013


For Smart UPS with Network Management Cards (AP9606, AP9617/18/19, AP9630/31), you'll need PowerChute Network Shutdown.

For Smart UPS with NO SmartSlot accessories installed (incase anyone is wondering) and for USB or serial communications, use PowerChute Business Edition.