Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

what is "low battery duration"?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • what is "low battery duration"?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:17 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
5
2333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:17 AM . Last Modified: ‎2024-03-18 11:23 PM

what is "low battery duration"?

I have a brand new UPS and I'm testing this but for the life of me I cannot figure out what this means.  I just had a 1.5 hr conversation with tech support and I'm still confused.  At first she said it was "how long to run on battery before notifying the PCNS clients", then she went into the lab and did 1/2 hr of testing and said it was "how long the UPS has battery power before it runs out".  

Help!

SW

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
0
2333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

Maximum required delay calculates the delay needed to ensure that each PowerChute client has enough time to shut down safely when the UPS or the PowerChute client initiates a graceful shutdown. Maximum Required Delay is the longest shutdown delay needed by any server listed as a PowerChute Network Shutdown client. This delay is calculated whenever the management interface of the UPS turns on or is reset, or when "Force Negotiation" is selected as Maximum Required Delay. "Force Negotiation" polls each client for information on the time it needs for a graceful shutdown. Two extra minutes to allow for unforeseen circumstances is then added to the calculated time. The negotiation can take up to 10 minutes. If you do not select "Force Negotiation", two minutes is used by default as the shutdown delay for all clients.

Example: you have configured PowerChute Network Shutdown to run a command file and the command file has a delay of 10 minutes when you click on force negotiation the maximum required delay will be changed to 12 minutes if your UPS does not have switched outlet groups. If your UPS has switched outlet groups then the outlet group power off delay that PowerChute is associated with will be increased.

SMT, SMX Smart-UPS have switched outlet groups.

On 8/28/2015 12:12 PM, Shawn said:

It seems to get set to the same value as "low battery duration" when you check off "force negotiation" and click apply. 

That is correct. If you change the low battery duration from the default of 2 minutes to say 8 minutes and click force negotiation the value of maximum required delay is increase to 8 minutes. Also, if your UPS has switched outlet groups the outlet group power off delay will be changed to match the value set for low battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
0
2333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

It is confusing. Imagine it says:

"When on battery and the estimated time before the battery becomes depleted drops below ____, tell everything it must shut down."

Or, using only the 10 hundred most used words:

"When using stored power and the best guess for time before the stored power is used up drops under ____, tell everything it must shut down."

So for example, your fully charged battery provides 45 minutes of electrical power. Suddenly your building experiences a power outage and only emergency lighting and your server remain on. Over time, the UPS' estimate of how long the battery will last decreases, because the server is consumer charge. We don't want the battery to run completely flat for a few reasons: because we want to safely shut down our server, we want to limit use of the battery to prolong its service life, and we want to have charge left over in case power comes back but fails again. So we set the low battery duration to 10 minutes. The power doesn't come back, so eventually the battery can only provide 10 minutes of electrical power. The UPS tells all devices they must shut down if they have not already. At this point, unsurprisingly, the battery can run for 10 more minutes, hence TS' answer. Smart devices attached to the UPS then shut down and tell the UPS to do the same. This take 4 minutes, so the UPS turns off when there's 6 minutes of battery life remaining. Later, power comes back, and when the battery charges to the point where it can provide the "minimum return runtime", the UPS output turns back on.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
0
2335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

Ahhh, ok that makes sense.  However, there's one more thing that is confusing:  You can set shutdown parameters on the client AND the UPS card.  In that case, which takes precedence?  For example, in th above scenario, what if I told the PCNS client to shut down 40 min. after a power outage?   The shutdown signal from the card would come at the 35 min. mark after the power went out.  But if I told it to wait 40 min, who wins?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
0
2335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

Hi,

Low battery would be reached before the On Battery delay and therefore would take precedence.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
0
2335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

Ok, that's good to know.  Just one more thing, what does "maximum required delay" mean and how does it get calculated?  This was another point of confusion when talking to tech support.   It seems to get set to the same value as "low battery duration" when you check off "force negotiation" and click apply. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

0 Likes
0
2334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:18 AM . Last Modified: ‎2024-03-18 11:23 PM

Maximum required delay calculates the delay needed to ensure that each PowerChute client has enough time to shut down safely when the UPS or the PowerChute client initiates a graceful shutdown. Maximum Required Delay is the longest shutdown delay needed by any server listed as a PowerChute Network Shutdown client. This delay is calculated whenever the management interface of the UPS turns on or is reset, or when "Force Negotiation" is selected as Maximum Required Delay. "Force Negotiation" polls each client for information on the time it needs for a graceful shutdown. Two extra minutes to allow for unforeseen circumstances is then added to the calculated time. The negotiation can take up to 10 minutes. If you do not select "Force Negotiation", two minutes is used by default as the shutdown delay for all clients.

Example: you have configured PowerChute Network Shutdown to run a command file and the command file has a delay of 10 minutes when you click on force negotiation the maximum required delay will be changed to 12 minutes if your UPS does not have switched outlet groups. If your UPS has switched outlet groups then the outlet group power off delay that PowerChute is associated with will be increased.

SMT, SMX Smart-UPS have switched outlet groups.

On 8/28/2015 12:12 PM, Shawn said:

It seems to get set to the same value as "low battery duration" when you check off "force negotiation" and click apply. 

That is correct. If you change the low battery duration from the default of 2 minutes to say 8 minutes and click force negotiation the value of maximum required delay is increase to 8 minutes. Also, if your UPS has switched outlet groups the outlet group power off delay will be changed to match the value set for low battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of