SURT8000XLI - configure delay for running servers back
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2802:18 AM. Last Modified: 2024-03-1811:23 PM
SURT8000XLI - configure delay for running servers back
Hello.
I have 2 SURT8000XLI UPS'es. Servers are connected to them redundantly. Yesterday power there was a power outage in company. I configured both UPS'es to gracefuly shutdown servers. When power was restored only one of servers turned on (rest of them had to be turned on manually).
I've checked if servers has set up POWER RESTORE options in BIOS and there were set "Always On".
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2802:18 AM. Last Modified: 2024-03-1811:23 PM
Hi,
Assuming the UPS outlets were providing AC to the servers the issue is with the servers themselves. You should contact the computers manufacture for support.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2802:18 AM. Last Modified: 2024-03-1811:23 PM
Hi,
Assuming the UPS outlets were providing AC to the servers the issue is with the servers themselves. You should contact the computers manufacture for support.