Hello.
I have 2 SURT8000XLI UPS'es. Servers are connected to them redundantly. Yesterday power there was a power outage in company. I configured both UPS'es to gracefuly shutdown servers. When power was restored only one of servers turned on (rest of them had to be turned on manually).
I've checked if servers has set up POWER RESTORE options in BIOS and there were set "Always On".
What is the problem ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:18 AM . Last Modified: 2024-03-18 11:23 PM
Hi,
Assuming the UPS outlets were providing AC to the servers the issue is with the servers themselves. You should contact the computers manufacture for support.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 02:18 AM . Last Modified: 2024-03-18 11:23 PM
Hi,
Assuming the UPS outlets were providing AC to the servers the issue is with the servers themselves. You should contact the computers manufacture for support.