voltage cut over for SUA2200 UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • voltage cut over for SUA2200 UPS
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
6
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:13 AM

voltage cut over for SUA2200 UPS

I am looking at the SUA2200 UPS and need it to have a cut over higher then 88v it would be great if it was 100v cut over but I can not find out if this can be changed from 82v to 88v or higher. Thank you for any help you can provide.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

JoeMomma wrote:
Keep in mind that your 100v requirement is for the output of the UPS, which is reasonable as most equipment won't run with anything less.

Your UPS, with its default settings, will not output anything lower than 103v, even if the input voltage is as low as 83v. Input voltage below 83v will force the UPS on-battery, which is a steady 120vAC output.

Remember that the UPS will boost (or trim) voltage if it's reaching the UPS outside of the acceptable output voltage range. It will try to boost or trim until 1) the voltage reaching the UPS is too low or too high to be adjusted on the fly, or 2) the input voltage returns to normal operating range to send UPS back to "normal" online mode.
Most decent IT equipment with a switch mode power supply should be fine down to 86v. 115v setting should accommodate Japan(100v) and India(127v) in addition to 110/120

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:13 AM

I am looking at the SUA2200 UPS and need it to have a cut over higher then 88v it would be great if it was 100v cut over but I can not find out if this can be changed from 82v to 88v or higher. Thank you for any help you can provide.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:33 AM . Last Modified: ‎2024-03-08 02:13 AM

Hi mepatuhoo,

The Smart-UPS family has adjustable transfer points on both the high and low side. These can be adjusted most easily via our PowerChute Business Edition software or a Network Management Card installed in the UPS.

Smart-UPS will first attempt to "boost" the incoming voltage if it reaches the UPS too low. If the voltage arrives too low to boost up near the nominal output voltage of 120v, the UPS will then transfer over to battery until the incoming voltage improves back to at least the adjustable boost range.

The same happens on the high side when voltage is too high when it reaches the UPS. We call that "trim".

Boost and Trim are the modes of AVR, or Automatic Voltage Regulation, technology implemented into this product.

By default, your 120v "4G" Smart-UPS has these low transfer points:
On Line to AVR Boost 106
AVR Boost to On Battery 82
On Battery to AVR Boost 87
AVR Boost to On Line 112

...and these high transfer points:
OnLine to AVR Trim 127
AVR Trim to On Battery 144
On Battery to AVR Trim 141
AVR Trim to On Line 122

You can reference this [kBase 715|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=715] to see how adjusting the high and low transfer points affects the transitions from online, to boost/trim, and to battery... and back the other direction.

So while the UPS may be receiving high or low voltages from utility, it always attempts to adjust or correct the output voltage via boost/trim or by switching to battery.

With the default settings, the lowest voltage your equipment would ever see is approx 103v, which is 83v * 24% boost. If the voltage reaches 82v, the UPS will switch to on-battery and output a steady 120vAC.

If you have any other questions, please let us know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

I am being told by another worker that the unit we will need should be at 100v lowend so if it get below 100v that it kicks into battery is this possible to do on this unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

Keep in mind that your 100v requirement is for the output of the UPS, which is reasonable as most equipment won't run with anything less.

Your UPS, with its default settings, will not output anything lower than 103v, even if the input voltage is as low as 83v. Input voltage below 83v will force the UPS on-battery, which is a steady 120vAC output.

Remember that the UPS will boost (or trim) voltage if it's reaching the UPS outside of the acceptable output voltage range. It will try to boost or trim until 1) the voltage reaching the UPS is too low or too high to be adjusted on the fly, or 2) the input voltage returns to normal operating range to send UPS back to "normal" online mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

Yes, that's right. Because it can take input voltages that are too low and "boost" them by up to 24%, the lowest voltage your load would "feel" would be about 103vAC. This is because the UPS will start "boosting" when input voltage reaches 106vAC by default. As input voltage continues to drop, the UPS will be boosting this voltage between 12-24% so that your load does not experience any voltages lower than 103.

If the input voltage were to reach as low as 83v, the UPS would be boosting by 24% which would give your attached load 103v, which is good.

If the voltage continues to fall below 83, the UPS will switch to battery operation, which always results in a steady 120vAC output until 1) the battery is exhausted or 2) the voltage returns to at least 87v, where the "boost" feature will again activate, thus yielding about 108v to your load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

0 Likes
0
665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:34 AM . Last Modified: ‎2024-03-08 02:13 AM

JoeMomma wrote:
Keep in mind that your 100v requirement is for the output of the UPS, which is reasonable as most equipment won't run with anything less.

Your UPS, with its default settings, will not output anything lower than 103v, even if the input voltage is as low as 83v. Input voltage below 83v will force the UPS on-battery, which is a steady 120vAC output.

Remember that the UPS will boost (or trim) voltage if it's reaching the UPS outside of the acceptable output voltage range. It will try to boost or trim until 1) the voltage reaching the UPS is too low or too high to be adjusted on the fly, or 2) the input voltage returns to normal operating range to send UPS back to "normal" online mode.
Most decent IT equipment with a switch mode power supply should be fine down to 86v. 115v setting should accommodate Japan(100v) and India(127v) in addition to 110/120

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of