vCenter server not shutdown cleanly by PCNS 3.1 and PCNS did not start when power was restored.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • vCenter server not shutdown cleanly by PCNS 3.1 and PCNS did not start when power was restored.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

0 Likes
3
2180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

vCenter server not shutdown cleanly by PCNS 3.1 and PCNS did not start when power was restored.

Hi,

I am hoping someone can help me understand why my vCenter server did not shutdown properly, and why the PCNS VM did not start when power was restored.  I will now describe our setup and observations made during a recent planned power outage.

I have 2 ESXi hosts running VMware 5.1.  They are in a HA cluster.

I am running PCNS 3.1 as a virtual appliance on the 2nd host.  vCenter Server is also running on this host.

My setup is the same as that outlined in Setup 1 A) outlined in the APC Application Note #180.

I have configured AD single sign on as outlined in the APC Application Note #180.  The AD login can login to each host using vSphere client. I can also see this user logging into each host every 2 minutes via the Events on vSphere client. (It is annoying to see this logging so often but that is another issue!).

We had a planned power outage on the weekend and the following events occurred (from the PCNS log)

  • After 10 minutes on battery power the UPS had a critical event (as planned)
  • Host 1 entered maintenance mode
  • Shutdown VMs on host 1
  • Host 2 entered maintenance mode
  • Shutdown VMs on host 2
  • Then after waiting for the configured amount of time to shut down the VMs I get the following messages
    • 08/23/2014         08:16:47      vCenter Server authentication error. PowerChute may not be able to issue commands to Virtual Machines or Hosts.
    • 08/23/2014         08:17:51      Cannot connect to vCenter Server. PowerChute will not be able to perform vApp Shutdown.
    • 08/23/2014         08:17:52      Cannot connect to vCenter Server. PowerChute will not be able to perform vApp Shutdown.
    • 08/23/2014         08:21:12      Shutting down Host Host1.
    • 08/23/2014         08:21:14      Shutting down Host Host2.

                     

From looking at the event logs on the vCenter Server it looks like it did not receive a shutdown command from PCNS.  Should I be expecting to see this graceful shutdown?

 

When power was restored the hosts powered up (due to BIOS settings) however PCNS virtual appliance did not start.  Host 2 was out of maintenance mode.  Host 1 was still in maintenance mode.

 

I was expecting the PCNS virtual appliance to be started by HA.

Any help would be appreciated.

Thanks

Janine

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • vmware
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

0 Likes
0
2180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

Hi Janine,

Is VMWare Tools installed on the Windows 2012 VM running vCenter Server?

On the Host Protection page do you see PowerChute/vSphere Icons for the 2nd Host? If you vMotion the vCenter Server VM to the first ESXi host does the Host Protection page update to reflect the change in location? If not then there may be an issue with locating the vCenter Server VM in the inventory.

With regard to HA failing to re-start the PCNS Virtual Appliance:

This is controlled by VMware HA Admission control. By default HA will not allow VMs to be powered on if they violate HA availability. If there is only 1 Host available (the other Host is in the cluster is in maintenance mode) then HA might not re-start the PowerChute Appliance:

2472_HA_Adm_Control.png

2473_ha_adm_control2.png

It may be necessary to disable Admission Control to allow HA to re-start the PowerChute Virtual Appliance. In the Tasks and Events view for the PowerChute VM are there any errors reported in relation to HA?

As mentioned in the App Note the maintenance mode task is cancelled and the PowerChute Virtual Appliance is powered off when the host goes down so that HA can "attempt" to re-start the Appliance when the Host is powered back. HA functionality is outside of the control of PCNS. To remove the dependency on HA re-starting the appliance so that VMs can be re-started outside of office hours an option would be to install PowerChute on a physical windows machine that is powered by the same UPS protecting the ESXi hosts and setting the BIOS on that machine to start automatically when A/C power is restored.

I will see that the information above is added to the Application Note.

In relation to obtaining the files you can use WinSCP to connect to the PowerChute Virtual Appliance and transfer the files over SCP/SFTP.

WinSCP :: Free SFTP and FTP client for Windows

I have sent you a Friend request via the Forum - once you accept that you will be able to send me the files directly rather than posting them publicly. If you have any issues obtaining the files please let me know.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

0 Likes
0
2180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

Hi Janine,

The issue with the frequent login events from PCNS in vSphere client will be addressed in the next release. It sounds like the vCenter Server VM is being shut down early along with the rest of the VMs and this is why the vCenter Server Authentication error message is appearing before the  vApp shutdown process starts. This may be occurring because PowerChute cannot locate the vCenter Server VM in the Inventory - it would explain why the vCenter Server VM is going down with the rest of the VMs and why there is no entry recorded in the PowerChute log to indicate that PCNS shut down the vCenter Server VM (the default delay for this is 240 seconds) before shutting down the ESXi hosts.

Could you provide a copy of error.log, pcnsconfig.ini and the full PCNS event Log please? These files are located in /opt/APC/PowerChute/group1 folder on the PCNS appliance.

On the VMware Host Protection page does the 2nd Host indicate that PowerChute and vCenter Server are present - there should be vSphere/PowerChute icons shown to indicate that the Host is running vCenter and PCNS as VMs? Do you see an option on the VM settings page to configure vCenter Server VM shutdown duration? Are you using Linux vCenter Server Appliance or is vCenter installed on a Windows Virtual Machine?

In relation to HA failing to start the PowerChute virtual appliance. This may be caused by HA Admission control settings - if there is only 1 Host available in the cluster (other host is in maintenance mode) HA may prevent any VMs from being started until the 2nd Host is taken out of maintenance mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

0 Likes
0
2180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

Hi drehan,

Thank you for your reply.

I don't believe the vCenter Server VM (this is a Windows 2012 VM) ever received a shutdown command.  I can see the shut down command in all of my other Windows VMs event logs but not on this one.

PowerChute and vCenter Server are both present on the 2nd host on hte host protection page.  I had configured the vCenter Server VM Shutdown duration to 240 sec.  As I stated above the vCenter is installed on a Windows 2012 VM.

HA failing to start PCNS - the App Note 180 says that maintenance mode is cancelled for the host running PCNS so HA can attempt to re-start PCNS when the host powers back on.  This is what I believed has happened except PCNS did not start.  If this is the way things are going to work then it is not very useful as we want PCNS to be up to be able to start the other VMs if the power outage happens out of office hours when IT staff are not here.

Files - we are new to PCNS virtual appliance and VMware so would appreciate some guidance on how to get the files requested off the PCNS VM.  I can login to the VM and navigate the folders and list the files.  That is as far as I can get.  Also is there a way I can send them directly to you rather than post them for everyone to see?

Thanks for your help..it is very much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

0 Likes
0
2181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 06:01 AM . Last Modified: ‎2024-03-04 11:58 PM

Hi Janine,

Is VMWare Tools installed on the Windows 2012 VM running vCenter Server?

On the Host Protection page do you see PowerChute/vSphere Icons for the 2nd Host? If you vMotion the vCenter Server VM to the first ESXi host does the Host Protection page update to reflect the change in location? If not then there may be an issue with locating the vCenter Server VM in the inventory.

With regard to HA failing to re-start the PCNS Virtual Appliance:

This is controlled by VMware HA Admission control. By default HA will not allow VMs to be powered on if they violate HA availability. If there is only 1 Host available (the other Host is in the cluster is in maintenance mode) then HA might not re-start the PowerChute Appliance:

2472_HA_Adm_Control.png

2473_ha_adm_control2.png

It may be necessary to disable Admission Control to allow HA to re-start the PowerChute Virtual Appliance. In the Tasks and Events view for the PowerChute VM are there any errors reported in relation to HA?

As mentioned in the App Note the maintenance mode task is cancelled and the PowerChute Virtual Appliance is powered off when the host goes down so that HA can "attempt" to re-start the Appliance when the Host is powered back. HA functionality is outside of the control of PCNS. To remove the dependency on HA re-starting the appliance so that VMs can be re-started outside of office hours an option would be to install PowerChute on a physical windows machine that is powered by the same UPS protecting the ESXi hosts and setting the BIOS on that machine to start automatically when A/C power is restored.

I will see that the information above is added to the Application Note.

In relation to obtaining the files you can use WinSCP to connect to the PowerChute Virtual Appliance and transfer the files over SCP/SFTP.

WinSCP :: Free SFTP and FTP client for Windows

I have sent you a Friend request via the Forum - once you accept that you will be able to send me the files directly rather than posting them publicly. If you have any issues obtaining the files please let me know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore