Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
using Powercute shutdown using vcenter with two host with cluster
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:00 AM. Last Modified: 2024-02-2910:57 PM
Fahad,
Page 70 of the users guide PDF lists a similar configuration. The difference is the PDF includes a storage array and you did not list one but the shut down steps are the same.
You should install PowerChute the system that vCenter Server is running on.
The following shutdown sequence occurs when the shutdown action is enabled for the On Battery event.
The UPS has been running on Battery power for x number of seconds.
PowerChute shuts down the VMs on VMware hosts A and B.
PowerChute starts a maintenance mode task on the VMware hosts.
PowerChute shuts down the VMware hosts.
PowerChute shuts down the vCenter Server application along with the system it is running on.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:00 AM. Last Modified: 2024-02-2910:57 PM
Fahad,
Page 70 of the users guide PDF lists a similar configuration. The difference is the PDF includes a storage array and you did not list one but the shut down steps are the same.
You should install PowerChute the system that vCenter Server is running on.
The following shutdown sequence occurs when the shutdown action is enabled for the On Battery event.
The UPS has been running on Battery power for x number of seconds.
PowerChute shuts down the VMs on VMware hosts A and B.
PowerChute starts a maintenance mode task on the VMware hosts.
PowerChute shuts down the VMware hosts.
PowerChute shuts down the vCenter Server application along with the system it is running on.