Please Help me for configuration of powercute shutdown for auto shutdown
i have vcenter on physical machine with two host with cluster
i want to shutdown VMs and host and vcenter too.
please guide me step by step how can i configure?????
Posted: 2021-07-08 01:00 AM
This reply was originally posted by Bill on APC forums on 7/8/2015
Fahad,
Page 70 of the users guide PDF lists a similar configuration. The difference is the PDF includes a storage array and you did not list one but the shut down steps are the same.
You should install PowerChute the system that vCenter Server is running on.
The following shutdown sequence occurs when the shutdown action is enabled for the On Battery event.
Posted: 2021-07-08 01:00 AM
This reply was originally posted by Bill on APC forums on 7/8/2015
Fahad,
Page 70 of the users guide PDF lists a similar configuration. The difference is the PDF includes a storage array and you did not list one but the shut down steps are the same.
You should install PowerChute the system that vCenter Server is running on.
The following shutdown sequence occurs when the shutdown action is enabled for the On Battery event.