I have a smart ups 3000 and i replaced the batteries since the LED on the front said to replace them. After replacing them it seems that the red light has not gone off. I also cannot access the management page on the NIC but that is a different topic. If i run a self test on the battery will it shut any of my servers off if there is still a problem with the battery? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:37 AM . Last Modified: 2024-03-13 01:39 AM
Hi Kirk,
Initiating a selftest via the button on the front panel should not cause the load to turn off if those batteries you installed are fresh ones.You just need to run a test to clear the replace battery indicator.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:37 AM . Last Modified: 2024-03-13 01:39 AM
Hi Kirk,
Initiating a selftest via the button on the front panel should not cause the load to turn off if those batteries you installed are fresh ones.You just need to run a test to clear the replace battery indicator.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.