sua1500rmi2u with ap9604/ap9604s
  • sua1500rmi2u with ap9604/ap9604s
Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM
882
Does anybody knows if the sua1500rmi2u compatible with ap9604 or ap9604s?
Also what cable is needed to connect to UPS with the AP9604 device? Cable 940-0024?
Txs,
Hi Jeroen,
Yes, you are correct on all accounts. Letter revisions of a cable just mean very minor changes, no change to pinout. You can use either.
And yes, this is a straight through serial cable as far as I know. i do not know if there any other specifics properties of the cable.
SUA models will likely work with AP9604. AP9604S will not work and is only for use with APC Silcon 3 phase UPSs.
From the UPS's DB-9 serial port, you need 940-1000 APC serial cable to plug into the port on the AP9604 that says "To UPS." Then, you can use 940-0024 or 940-1524 on the advanced port on the AP9604 to connect serially to the UPS or any supported accessories you may connect, such as a UPS Network Management Card.
Hi thank you,
I was searching and found that there is a 940-1000A and 940-1000B. Is there a difference?
Is it right to say that there is no wiring difference between the two cables?
Is it right to say that the 940-1000 is a simple straight through cable?
Txs.
Hi Jeroen,