7901 with port’s 5 & 6 stuck on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • 7901 with port’s 5 & 6 stuck on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
3
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

7901 with port’s 5 & 6 stuck on

I have a 7901 with ports 5 & 6 stuck on; you go into management page and turn the ports off, the LEDs cycle off but power still is at the receptacle. Is there anyway of testing to see if it’s a hardware error or getting the relays to cycle?

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • 7901
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

No, there is no issue with keeping them off but the relays in the PDU are only designed for XXXXX amount of switches/cycles. I forget what the exact number is but these are definitely not designed to be constantly cycling 24/7.

What you describe is probably what many other users do also (lab environment). I don't think what you're specifically doing personally is causing a problem. Off the top of my head and based on experience, factors leading up to this type of failure include age, number of cycles, current on each outlet, etc or a combination could contribute to this type of failure. Of course, a tiny percentage could always be because the relay was defective from the start which we'd cover under the factory 2 year warranty on the PDU anyway.

Do you think the PDU is under warranty? I could help you determine that by the first six characters of the serial number.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

This sounds like some type of relay weld. Do these get cycled on/off frequently and have high current devices connected? Depending on warranty status, sometimes you may be able to "shake" these loose but it could potentially weld again.

I would say if anything, its definitely a hardware issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

Right now the ports only had smaller network devices on them, so pretty low power. But, alas I am not the original user, so I can not attest to their usage in the past and I just built up the rack to test some ideas on. I have really never thought about duty cycle on the relays before. Since this hardware is non production and only used testing ideas, is there any issue with ports mostly being off? Basically everything is kept off until we need to build a test environment, it might for be run for the day and turned off at night, it might be run for a few days, it might been off for weeks at a time, or I could spend my day simulating power issues and cycling the equipment on and off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

0 Likes
0
866
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:03 AM . Last Modified: ‎2024-03-18 12:56 AM

No, there is no issue with keeping them off but the relays in the PDU are only designed for XXXXX amount of switches/cycles. I forget what the exact number is but these are definitely not designed to be constantly cycling 24/7.

What you describe is probably what many other users do also (lab environment). I don't think what you're specifically doing personally is causing a problem. Off the top of my head and based on experience, factors leading up to this type of failure include age, number of cycles, current on each outlet, etc or a combination could contribute to this type of failure. Of course, a tiny percentage could always be because the relay was defective from the start which we'd cover under the factory 2 year warranty on the PDU anyway.

Do you think the PDU is under warranty? I could help you determine that by the first six characters of the serial number.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore