snmp OID to pull out the UPS Load on the Smart-UPS 1000 ?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • snmp OID to pull out the UPS Load on the Smart-UPS 1000 ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
12
6413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

snmp OID to pull out the UPS Load on the Smart-UPS 1000 ?

On the Smart-UPS 3000 I am able to use the OID .1.3.6.1.4.1.318.1.1.1.4.2.3.0 to pull out the UPS Load.

But this OID does not work on the Smart-UPS 1000.

Does any one knows the correct OID to pull out the UPS Load on these Smart-UPS 1000 ?

Thank you

Antonio Feijao

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

You're welcome. Hope you have a nice weekend too laughing

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

What response did you receive from upsAdvOutputLoad on the Smart UPS 1000 specifically?

What does the web or telnet/SSH interface show for the current load percentage? This value would be the load percentage and should work on majority of UPS models.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

Hi Angela

on the webpage show the correct load, 13% when I checked, but the OID does not work for this UPS model, so I was wondering if someone knew the correct OID to use with the UPS 1000 serias

----------------------------this is OK ----------------------

snmpwalk -v 2c -c public ***IP****...123 .1.3.6.1.4.1.318.1.4.2.2.1.5.1

SNMPv2-SMI::enterprises.318.1.4.2.2.1.5.1 = STRING: "Smart-UPS 3000"

snmpwalk -v 2c -c public **IP**.123 .1.3.6.1.4.1.318.1.1.1.4.2.3.0

SNMPv2-SMI::enterprises.318.1.1.1.4.2.3.0 = Gauge32: 43

----------------------------- this with UPS RT 1000 is NOT OK ------

snmpwalk -v 2c -c public ***IP***.124 .1.3.6.1.4.1.318.1.4.2.2.1.5.1

SNMPv2-SMI::enterprises.318.1.4.2.2.1.5.1 = STRING: "Smart-UPS RT 1000 XL   "

snmpwalk -v 2c -c public ***IP***.124 .1.3.6.1.4.1.318.1.1.1.4.2.3.0

SNMPv2-SMI::enterprises.318.1.1.1.4.2.3.0 = No Such Instance currently exists at this OID

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

Ok, you did not mention it was an RT and I should've asked embarassed since we have a regular 1000 and then Smart UPS RT 1000. I have an explanation I can provide to you now that I understand model it is.

In NMC1 v2.5.3 or lower firmware, the OID (.1.3.6.1.4.1.318.1.1.1.4.2.3.0) for upsAdvOutputLoad, was retrieving the UPS output wattage value. However, in NMC1 (AP9617/18/19) or NMC2 (AP9630/31) v2.6.4 or higher, the OID started retrieving the VA value instead with SURT series.


The SURT 1000/2000 does not support certain data values, so these two don't report Iout amps, even though the larger SURT models do. They will however report % Wattage without issue.


Because of these, the SNMP value reading from upsAdvOutputLoad shows 0 with SURT1000/2000 when the NMC is running the firmware v2.6.4 or higher.


With NMC2 sumx APP v5.1.5 or higher, the percentage of VA and output current have been properly removed from all interfaces including the web, CLI, and datalog. In SNMP, that means that output current SNMP OIDs (upsAdvOutputCurrent and upsHighPrecOutputCurrent) are no longer supported and will report back No Such Name.


For output load OIDs (upsAdvOutputLoad and upsHighPrecOutputLoad), the highest percent VA, if supported, or percent watts, across all output phases, gets reported. This is true regardless of the UPS communication language.


So, to help further, what model management card are you using and what is the firmware on it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

Hi Angela,

thank you for your help

Please find below more details about the device

American Power Conversion               Network Management Card AOS      v3.7.3

(c) Copyright 2009 All Rights Reserved  Smart-UPS & Matrix-UPS APP       v3.7.2

-----------------------------------------------------------------------

        About System

        Model Number      : AP9618

        Serial Number     : xxx

        Manufacture Date  : 09/12/2008

        Hardware Revision : A10

        MAC Address       : xxxx

        Flash Type        : AMD A29DL322DB

        -----------------------------------------------------------------------

        Module Information

        Description : Smart-UPS & Matrix-UPS APP

        -----------------------------------------------------------------------

        Name        : sumx              Type        : StatApp

        Version     : 372               Sector      : 16

        Date        : 02/02/2010        Time        : 19:08:16

        CRC16       : EFCA

        Description : Network Management Card AOS

        -----------------------------------------------------------------------

        Name        : aos               Type        : APC OS

        Version     : 373               Sector      : 47

        Date        : 02/02/2010        Time        : 17:05:14

        CRC16       : B630

------

from web interface

About UPS

Model:Smart-UPS RT 1000 XL
Position:x
Serial Number:xx
Firmware Revision:411.8.I
Manufacture Date:07/12/08

Hardware Factory

Model Number: AP9618

Serial Number: xxx

Hardware Revision: A10

Manufacture Date: 09/12/2008

MAC Address: x

Management Uptime: xx

  

Application Module

Name: sumx

Version: v3.7.2

Date: 02/02/2010

Time: 19:08:16

APC OS (AOS)

Name: aos

Version: v3.7.3

Date: 02/02/2010

Time: 17:05:14

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

I don't have one of these readily available or else I would just check but I am thinking we should check everything else under upsAdvOutput and upsHighPrecOutput and see what works. Otherwise, if this is super critical and you wanted it, we'd have to downgrade your firmware which I would not recommend just for this cause you'll probably run into other issues.

I might be able to track one down shortly to verify myself.

Edit: So here in NAM I have an SURTA1500XL I tracked down with an AP9619 (same NMC firmware as your AP9618) which I thought was the same UPS-wise and I put a load on it and upsAdvOutputLoad is reporting back 80 (%). It must be different than the XLI model you have...?

1266_%241E9C85380966A948.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

You're welcome. Hope you have a nice weekend too laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

Hi,

no, not having this feature is not critical, I was just wondering if there was a correct OID to collect this information on this versions. Your explanation are very clear, so thank you for that. Your help was very useful.


Thank you and enjoy your weekend wink

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:44 PM

Sorry, before going to weekend, I saw that you have edited your reponse

snmpwalk -v 2c -c public **IP**.124 | grep upsAdv

( I got no results. on this command...) I not sure if a can run oid in the command line without the ....1,.1.1.1.1 numbering convention... can you provide the OID number that you were using there ?

thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:43 PM

0 Likes
0
6412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:53 AM . Last Modified: β€Ž2024-03-05 10:43 PM

Sure.. The values you see are respectively in the same order below.

.1.3.6.1.4.1.318.1.1.1.4.2.1 (voltage)

.1.3.6.1.4.1.318.1.1.1.4.2.2 (Frequency)

.1.3.6.1.4.1.318.1.1.1.4.2.3 (load)

.1.3.6.1.4.1.318.1.1.1.4.2.4 (Current)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-07-01 03:54 AM . Last Modified: β€Ž2024-03-05 10:43 PM

0 Likes
0
6411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:54 AM . Last Modified: β€Ž2024-03-05 10:43 PM

.3 (load) and .4 (Current) didn't work... so there now solution to get the Load in this UPS ? (Apart from downgrade the firmware)

snmpwalk -v 2c -c public ***IP*** .1.3.6.1.4.1.318.1.1.1.4.2.1

SNMPv2-SMI::enterprises.318.1.1.1.4.2.1.0 = Gauge32: 229

snmpwalk -v 2c -c public ***IP*** .1.3.6.1.4.1.318.1.1.1.4.2.2

SNMPv2-SMI::enterprises.318.1.1.1.4.2.2.0 = Gauge32: 49

snmpwalk -v 2c -c public ***IP*** .1.3.6.1.4.1.318.1.1.1.4.2.3

SNMPv2-SMI::enterprises.318.1.1.1.4.2.3 = No Such Instance currently exists at this OID

snmpwalk -v 2c -c public ***IP*** .1.3.6.1.4.1.318.1.1.1.4.2.4

SNMPv2-SMI::enterprises.318.1.1.1.4.2.4 = No Such Instance currently exists at this OID

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-07-01 03:54 AM . Last Modified: β€Ž2024-03-05 10:43 PM

0 Likes
0
6411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:54 AM . Last Modified: β€Ž2024-03-05 10:43 PM

I guess not...? Strange why the domestic model here does respond to the upsAdvOutputLoad OID but yours does not. Nevermind the fact that yours displays it in the web UI but not via SNMP. Part of it might have to do with you having an older card too so an NMC2 might display this value via SNMP for your UPS model. I don't suppose you have an AP9630/31 to test with in this UPS just to see if it responds?

Since I don't have an SURT1000/2000XLI, I'd say just walk the entire UPS tree or look at it with a MIB browser and see what you get. I can do that there on my SURTA1500XL and I would do it to give you answer but mine is different apparently cry

Reply

Link copied. Please paste this link to share this article on your social media post.

wieste_apc
wieste_apc
Cadet

Posted: β€Ž2021-07-01 03:54 AM . Last Modified: β€Ž2024-03-05 10:43 PM

0 Likes
0
6411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-07-01 03:54 AM . Last Modified: β€Ž2024-03-05 10:43 PM

Hello

I've found this thread via google, I've the same problem 😞

Have you found a solution?

Thank's a lot

Stefan

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore